I agree with Westy, the circuits cannot now be independently isolated, anyone working on the RFC in the future could potentially get a shock from the cooker circuit in the event of a fault on the cooker.
It is as BL says like borrowing a neutral, as soon as that link is disconnected there could be a potential difference between the two earth conductors.
Big problem with temporary repairs is that they have a nasty habit of become permanent repairs!
Also, what has now been done must surely screw the test results for the RFC, so how do you document that in the EICR?
Correct thing to do would be to isolate the cooker circuit and label it saying it is not to be used until remedial action has been carried out and document that to the client.