Discuss IT Equipment PAT testing in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net
dwedge
When called into Pat test a factory shop floor equipment, the question was asked do Comptuers screens and printers need to be tested, If this is the case what kind of test (Class 1,2 or 3 ) apply. As we know some PC`s still have an earth conductor, so I assume it is Class 1. Please could anyone give me concrete information to show to client...Many Thanks DWEDGE
you can perform a lower voltage test if the lead is moulded in, if not you can remove the lead and test this only. my guide is down in the car but i'll have a look tomorrow for you and confirm 100% then :)
but i believe the monitor should be tested if it is CRT because of the high running internal voltages or something to that effect
Any decent PAT tester like Seawrds or Megger have a seperate tests for IT equipment built into the program for the machine.
1. Having a CPC doesn't make equipment Class 1, it just means it has a cpc.
2. Class II require touch current test, not Insulation Resistence.
3. Earth Leakage current might be expected from some appliances, such a swith Mode PSU so don't bother with above if that's the case.
4. CRT can have anything up to 32kV on the flyback transformer. If that's leaking you'll know long before the PAT monkey comes around. ID the CRT PSU and then decide what test to perform. May IR, maybe Touch.
5. Visual inspection of Class II is acceptable. Test what you can (removable leads etc.)
6. All of the above may be cobblers as it's been a while since I avoided PAT testing
7. I hate PAT testing and how it's being slavishly carried out, largely by people with no more idea of what to do than they have of what it's for and before anyone flames me for that I' include myself in that statement as a former PAT monkey.
8. I got out the wrong side of bed this morning...
Reply to IT Equipment PAT testing in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net