Discuss Iz not greater than In in the UK Electrical Forum area at ElectriciansForums.net

Shpark

-
Reaction score
10
I'm doing some calcs for college and need a little help.

So, Iz has to be greater than In, but I'm not achieving this.

My totals watts for a lighting circuit is 354w

So 354/230=1.54

Ib=1.54A

In=6A for lighting CPD

Correction factors of:-

Ca - 0.91
Cg - 0.7

Iz = 1.54/(0.91x0.7) = 2.4A

What do I do?

Cheers
 
You have worked out the current, you now need to select the correct cable and protective device.

Looks like you're getting confused, Iz is current carrying capacity, In is the current setting of protective device.

You have calculated Ib which is the design current.
 
Are you getting a little confused between Iz and It. Page 333 of BS 7671 equation 2 states to work out the value of It you divide In by the correction factors. In your calculation you divided Ib by the correction factors. By using In you will always satisfy the requirements of regulation 433.1.1 of BS 7671.
 
I have picked the protective device at 6A MCB and 1.5mm cable

How did you select the cable size without completing the cable size calculation?

You’ve divided Ib by the de rating factors where you should be dividing In by the de rating factors.
So It=In/(Ca.Cg)
Once you have done that you can use Iz to select your cable size from the tables.

It’s also worth noting that It doesn’t necessarily have to be greater than In, the rating factor Ca for example can be greater than 1 for low temperatures so can result in a lower It than In.
 
the Iz for 1.5mm cable, clipped direct is about 19A. that's where you done gone wrong.
 
At college I've always been taught that Iz=Ib/Cg x Ca

This is an example of what we do...attached
 

Attachments

  • Question 5.pdf
    348.6 KB · Views: 103
Last edited:
At college I've always been taught that Iz=Ib/Cg x Ca

This is an example of what we do...attached

Then I’m afraid to say you may have misunderstood, or your college are teaching you incorrectly.
It can be calculated by this method if overload protection is not required, but not Iz

Iz is the current carrying capacity of a cable, this can be calculated by multiplying the tabulated current carrying capacity by the rating factors. This is explained in the appendix to the regulations along with the reasoning for why we rarely carry out this calculation, normally It is calculated to establish the required conductor size.
It should be greater than or equal to In divided by the rating factors.
 
hi there everyone this is my first post here so be patience whit me.. Im doing the electric course and im doing my assessment and in need of some help.
for my understand iz=in/CaxCgxCi......
then it is from the tables 4D2A Correct?
on the images I add I did some of the calculations but I start to think im doing something wrong. can you clarify it for my.. like do I need to fill the iz when im doing a ring final?
Thanks for help...
 

Attachments

  • IMG_0620.JPG
    255.6 KB · Views: 79
  • IMG_0621.JPG
    210.6 KB · Views: 56
  • IMG_0622.JPG
    230.9 KB · Views: 46

Reply to Iz not greater than In in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, this is driving me mental, if I have a Ca of 1.03 (25degrees ambient) & a In of 6A or any number you like then Iz will never come out...
Replies
19
Views
2K
not to sure on how to find the wats for the power cable calcs could anyone help me its for a ring with 3 Dubble sockets on DB05-3L2 cable size...
Replies
4
Views
1K
Hi I'm currently doing C&G 2365 Level 3 I'm working through the 305 design assignment (Swimming pool, hotel etc.) Other then this assignment I...
Replies
4
Views
4K
Hi everyone, I'm new here and was wondering if someone could help to get my college project calculations right. I'm about to start my 2nd year in...
Replies
12
Views
7K
So I've calculated my hotel lighting and 1 circuit has an (ib) of 0.33a and I put a 6a breaker on it (in) then got my (iz) 5.8a which is suppose...
Replies
1
Views
794

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock