Induction and oven have a theoretical max draw of 46a. Whilst this is unlikely to be drawn at the same time it seems a safer bet to install 10mm cable rated for 40-70a as this is a permanent addition.

It will never happen. Ovens cycle. Read up on diversity.
 
Induction and oven have a theoretical max draw of 46a. Whilst this is unlikely to be drawn at the same time it seems a safer bet to install 10mm cable rated for 40-70a as this is a permanent addition.

It will never happen. Ovens cycle. Read up on diversity.
 
You will not save anything cost wise by dictating cable sizes to an electrician.
A 32A rfc in 2.5mm will probably suffice, as it does for the majority of homes in the uk.
Dedicated radial for cooker, and maybe for w/m and another for freezer.

Personally, don’t do a grid switch. Too fiddly to work with, but I would have a 20A dp switch controlling unswitched sockets in adjacent cupboards, not behind appliances.

If your electrician designs the circuits, any comeback will be on his head, not yours.
now you have design it for him you as well go and do the job has well.
 
You will not save anything cost wise by dictating cable sizes to an electrician.
A 32A rfc in 2.5mm will probably suffice, as it does for the majority of homes in the uk.
Dedicated radial for cooker, and maybe for w/m and another for freezer.

Personally, don’t do a grid switch. Too fiddly to work with, but I would have a 20A dp switch controlling unswitched sockets in adjacent cupboards, not behind appliances.

If your electrician designs the circuits, any comeback will be on his head, not yours.
now you have design it for him you as well go and do the job has well.
 
For someone not doing the electrical design or installation, you are going into depth electrical terminology for the kitchen.
 