chloebear

Just been on site carrying out some additional works in a Grade 2 listed building and noticed that the consumer unit (16way Hager board) has had a large part of the rear of the casing removed for cable entry from behind. The board is mounted direct onto the wall which is lath & plaster.

The question is - should this be sealed to avoid it being a fire risk???

are there any regs that cover this??
 
thinkhe's more concerned with fire risk, with the board being mounted on lath and plaster wall.
 
Is there a difference between doing it that way and mounting it on a bit of plywood? The hager boards come with all the cutouts for you as you need them. As long as it is to ip2x then I can't see the issue
 
Hmmm, i take it you have never seen a Wylex CU that came with no back at all and had a wooden frame?? In fact i'd go as far as saying that those old Wylex CU's would stand up to a fire, far better than any of these modern plastic IP2X CU's.... lol!!
 
Please don't give the regs writers the idea we need to plug the rear of CU's

Its been there from the beginning lol
There is a tick box on your EIC sheet.

Guidance notes 1

reg ref 527.2.4 & 527.2.1

5.8 Sealing and fire stoppingWhere a cable, conduit, trunking or busbar trunking system passes through a building wall or floor slab it is necessary to seal the hole around the cable, etc., to the standard of the original wall or slab to prevent the passage of moisture, condensation, vermin or insects, etc. The sealant must be suitable for the cable, etc. and the environment and should be flexible to allow some small movement of the cable, etc., relative to the building. Seals should be installed when necessary to maintain the building integrity during construction.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Large unsealed cable entry at rear of CU
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7
Unsolved
--

Advert

Thread statistics

Created
chloebear,
Last reply from
Simlec,
Replies
7
Views
1,217

Advert

Back
Top