S

Stevesplatto

Hi,
I'm installing lighting system in a garden. the client wants 5 LED brick lights installed in a L shaped, 2 course wide dwarf wall.
I'm thinking of running 2core 1.5 SWA under the unbuilt patio to an ip44+ enclosure on the side of the wall then run 0.75 rubber sheafed 'pond' cable (really flexible, got me out of many a tight spot.) in the cavity to the back boxes using glands to maintain the IP rating..
Do I have to provide any extra protection in this case as it's protected by the wall and above ground?

Cheers
S
 
i there's room in the cavity, i'd use 20mm pvc conduit.
 
Should be OK, run the SWA in a duct so it can be replaced if necessary and put warning tape above it.
The rubber flex so long as it is correctly glanded to the SWA and the enclosure of the light fittings will be OK as is but conduit would be neat.
 
what are these ''BRICK'' lights like? do you mean the light fitting fit's into the standard space of that of a brick?
 
Yep, they come with a standard brick size back box. I've asked for the wall to be built up to the level of the brick lights. I drop the cabling in (plus the pvc conduit now!) the wall gets built up and coping laid on top.
SWA is laid in trenches, warning tap on top. Duct not practical but access not too fifficult if proble (lift patio slabs).
Thanks for the response
s
 
And from where does one purchase the dwarfs with which to build this wall? I have been in many a builders merchants and never seen them for sale,or do you have a branch of dwarfs R us near you?









Sorry lads theres been that much arguing on this forum lately I couldnt resist a light moment.
 
I get them at the new Screwfix Metros that are popping up all over the place. Ideal for height challenged accesories :smile:
 
What I would do is fill your IP44 adaptable boxes with magic gel or resin ,always find the dam things fill up with water
 
Personally I would use SWA terminated in a Y box within the cavity with a little slack on the SWA's. if these are positioned behind the brick lights then it is fairly easy to remove the fitting and bring the box out of the wall for maintenance testing etc.
 