R
RedSnedd1903
Hi everyone. First time poster here so go easy. I have a lighting circuit on an installation I'm working on that is giving me some grief. There are 50 x 4W gu10 LEDs on one switch and it keeps tripping the 6A mcb. The total load of the lamps is not even 1 amp. There are other lights on the circuit but the total load comes to about 5A. Insulation resistance check on both switch wires are both clear>299. It happens every 2nd or 3rd time that the Led D/lts are switched on. Even when all other lights on the circuit are switched off. I've tried replacing the circuit breaker but still the same happens. Has anyone else had any problems like this.
cheers
Al
Startup current on LEDs is usually quite high. 50 down lighters on one circuit sounds like too many as well.
Definately high inrush,If things allow you may get away with changing from a type B to a type C breaker,you'd need to check your Zs first mind but it seems a lot on one circuit.
This was what I was wondering, is it too many lights even though even though they are low wattage LEDs . I had a clamp meter on the supply feed at the mcb whilst switching the lights on to see if there was a spike in the current but it never went above 1A.
50 LED's on one circuit/switch - NOT a good design. In rush will be your problem. Maybe try a 10A.
Edit: so who designed this? Design calcs should "assume" 100w per point so that would be 5000 watts or about 21 amps. OOPS
Looks like it will be a c6 mcb getting used. The design was done by another electrician who's currently off shore. I'm just helping out whilst he is away. The max Zs measured at the last light is 2.35ohms.