Discuss Low IR ring final circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
robo83
Testing a ring final circuit today. R1+R2 is fine, same as end to end r1 rn and r2.
However IR test is coming back 1.87M ohm. I split the circuit and located a section (one side of the ring is clear >999).
The customer doesn't want any walls or ceiling touched. As this is greater than 1M ohm can this be left and simply noted on cert.
are you doing a EICR? if so, then you just record what is there. it's a report . it's then up to the customer, considering your advice as an expert, to decide what to do about it. your remit does not cover fixing anything. you're just providing a report.
Reply to Low IR ring final circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite...
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...