So Ze=0.02 and R1+R2 = 0.73 on a first floor ring main.

Nearest submain is about 35m away, so that Ze's plausible, and even a slightly indirect route makes Ze=0.03 realistic. So MCBs are going to need changing to Type Cs.

Unfortunately for that first floor ring R1+R2 of 0.73 is too high for a 32A Type C. Yes I've got behind every point on the circuit, empty house so nothing hidden, no poor connections there, perhaps a JB hidden away under the floor somewhere but I'm not about to tear apart a (very nicely done up) house on a maybe when there's simpler things to do.

My first thought is "aha, but it is low enough for a 20A Type C!" which is how I intend to go about it right now, should still be enough power I think.

The idea I've just had though, and forgive me if this is dumb, it's late alright? is to split the circuit into two radials, so that one side goes to the large room at the front and the other goes to the two bedrooms, and put them on 16A breakers, allowing for more current overall if slightly less max load in each area.



TLDR: Low Ze, needs changing from Type B to Type C breakers. Either cut 32A ring with R1+R2=0.73 down to 20A or make into two 16A radials?

Thoughts?
 
End to end L=0.91 , N=0.90 , CPC=1.94

Yes the CPC seems a bit high, hence my suspicion that there's a JB somewhere under the floor since I've been round all the visible points.



However I've also just figured out that I can't split the circuit!

At the middle point of the circuit, resistance-wise, if I split it there it's effectively halving the CSA of the wire, and hence doubling the resistance. So then I would need to bring it down to two 10A breakers!

Like I said, it's late, tired Matt is dumbass Matt! Keeping the ring and making it a 20A Type C... *facepalms*
 
On the other hand, the other circuits all look like typical 2.5 1.5... got 0.89/0.90/1.42, a 0.36/0.38/0.64, and a 0.62/0.61/1.01.

At a glance the cables all look the same so I would've thought they were put in at the same time, will have another look but still betting on a long-lost JB is lurking under a floor somewhere.
 
Oh sorry must've mis-typed westward.

Low Ze so changing to type C.
Zs too high on one circuit to keep it on a 32A.
Was toying with the idea of splitting the circuit into 2 16A radials.
Realised that splitting the circuit would increase the resistance so couldn't use 16A Type C radials.
Back to original idea of making it a 20A Type C ring.
Much wittering to ensue.
 
The cpc reading is high assuming the cpcs are 1.5 as you should probably expect 1.50. But even with that the Zs is likely to be too high for a Type C 32A. Further investigation and fit a Type B 32A but as Doc says you could have 1.0 cpcs in circuit.
 
Changing from a B to C type MCB is a a non-starter on general use socket outlets in my opinion. You are at least doubling the minimum trip current.

Is the circuit on an RCBO? As such I would
probably leave it as is and note on the cert that due to exising high earth loop impedance measurments the RCBO is being used as fault protection and the Max permitted Zs is then 1667.
 
Is the circuit on an RCBO? As such I would
probably leave it as is and note on the cert that due to exising high earth loop impedance measurments the RCBO is being used as fault protection and the Max permitted Zs is then 1667.

Isn't that just for a TT arrangement?
 
Isn't that just for a TT arrangement?
Generally yes whereby a protective device alone does not provide fault protection. Using one for fault protection on a TN system is considered bad practice as you are essentially compensating poor circuit design with an rcd, on a TN system a 30ma rcd is for additional and not fault protection.
This thread however is somewhat bizarre.
 
Generally yes whereby a protective device alone does not provide fault protection. Using one for fault protection on a TN system is considered bad practice as you are essentially compensating poor circuit design with an rcd, on a TN system a 30ma rcd is for additional and not fault protection.
This thread however is somewhat bizarre.

Completly standard design when high loop impedances are an issue on a TN system.

I agree if designed to be used as fault protection on a decent enough Ze then that is poor design however this is an existing installation and the exisiting poor design is no fault of the op so a bit of common sense needs to prevail.
 

Reply to Low Ze, high(ish) R1+R2, Got a plan but just had an idea in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock