Ran into a very similar issue today in a nasty Barratt flat. Ze of 0.08, but L-N 0.03 according to my Megger, though it gave me a calculated pfc of 6.3k which suggests it was calculating to more digits than it was showing me.
Anyway, sub main to the flat 16mm T&E protected by a 63A MCB with 6kA rating. Also a main fuse somewhere, but not in the same building it appears (red fuselink).
Given that the source feed is an MEM enclosure with MEM breaker, and the flat board is LeGrand throughout, I'm assuming I can rely on the type testing for 16kA so no need to consider coding in my case.
As pointed out, the extra 0.01 can make quite a difference.