Discuss Lowest Zs reading and highest PFC i've seen. Answers on a postcard please..... in the UK Electrical Forum area at ElectriciansForums.net

D

DaveyLe_Spark

I did an EICR for a client over a year ago and as part i took the Ze reading at the incoming supply. All normal for a TNC-S it was about 0.14 ohms. I installed a socket in his workshop recently and as his tenant was in i could not remove the main earth so i took a Zs at the same position. The Zs reading came out at 0.01 ohms (the property is right next to the sub station) My issue now is that with a Zs so low it is giving me a PFC of over 14.5kA. I looked into replacing the MCB's for D-Type. Most of the values of circuit Zs are ok but a couple are higher than the stated regs. Although these are covered by a 30mA RCD, there are a few RCBO's in there which are not available as a typr D to withstand that potential in rush in the case of a fault. I also cannot find any literature on the fault rating of the main switch and RCD's in the board too. The make is M2 (CEF) I have called my registered body and they cannot suggest anything, i thought about putting some sort of resistor in line with the structural steel bond (which is the one causing this headache i believe) but i am not sure on the regs for doing that. It just seems all wrong! Has anyone come across this before and does anyone else test both Ze and Zs at the main board? I was only ever taught to take a Ze as required by the certs but i will take both from now on!

Thanks in advance.

Dave.
 
As long as the main intake fuse can stand the Huge Pfc ,then all is fine.Usually a 1361 type 2, thinking it's rated at 16ka is ok.the DB would also have that rating too.
 
Last edited:
Type D breakers are only designed to cope with a normal overload current that is briefly high not a fault current that is high.
You would need to select breakers with a higher breaking capacity to do what you are doing.
I.e. the Icn should be sufficiently large to cope with the fault current without failing.
However most domestic breakers are 6kA or perhaps 10kA.
However as cliffed has said is you have a consumer unit and a main fuse as a BS1361 then it is considered sufficiently safe up to 16kA.

With a low Zs it may be an idea to measure as stated in this thread to ensure you have a correct value.
 
I did an EICR for a client over a year ago and as part i took the Ze reading at the incoming supply. All normal for a TNC-S it was about 0.14 ohms. I installed a socket in his workshop recently and as his tenant was in i could not remove the main earth so i took a Zs at the same position. The Zs reading came out at 0.01 ohms (the property is right next to the sub station) My issue now is that with a Zs so low it is giving me a PFC of over 14.5kA. I looked into replacing the MCB's for D-Type. Most of the values of circuit Zs are ok but a couple are higher than the stated regs. Although these are covered by a 30mA RCD, there are a few RCBO's in there which are not available as a typr D to withstand that potential in rush in the case of a fault. I also cannot find any literature on the fault rating of the main switch and RCD's in the board too. The make is M2 (CEF) I have called my registered body and they cannot suggest anything, i thought about putting some sort of resistor in line with the structural steel bond (which is the one causing this headache i believe) but i am not sure on the regs for doing that. It just seems all wrong! Has anyone come across this before and does anyone else test both Ze and Zs at the main board? I was only ever taught to take a Ze as required by the certs but i will take both from now on!

Thanks in advance.

Dave.

This may also have an implication for protective conductor sizes (see 434.5.2 of BYB and table B7 of OSG, although the later only includes up to 6kA).
 
As Richard Burns suggests, use the alternative method for measuring Ze using a known resistance. With really low impedance readings your instrument inaccuracies increase and the alternative method will give you a more realistic result.
 
Thanks for your response. I have looked further into this and i contacted the manufacturer (Proteus) Up until late last year the braking capacity of the main switch was 2kA and the Rcd's still is 4.5kA. Late last year when the new regs amendment was imminent they all now have to be manufactured to a different BS, ensuring that all breakers and the main switches have a 16kA capacity. I will source some B type from this new batch and hey presto, problem solved.
 

Reply to Lowest Zs reading and highest PFC i've seen. Answers on a postcard please..... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone Recently I have come across an advert of someone selling Afdds C type and the person mentioned the need to sell because Zs was too...
Replies
16
Views
3K
Hi First time with this kind of a job for me. I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
Replies
32
Views
6K
I hope someone can help me as im getting different answers off different people 3P & N Supply Ze: Disconnect main earth Set tester to 2 lead...
Replies
29
Views
7K
The purpose of this thread is two-fold: to let you folks see an EICR from someone who's too lazy (or busy) to even bother forging his test...
Replies
15
Views
3K
Hi everyone, a few questions here Ze: In the AM2 is it just a 2hi test between L1 - Earth, L2 - Earth and L3 - Earth. Then take the highest...
Replies
36
Views
9K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock