DaveyLe_Spark
I did an EICR for a client over a year ago and as part i took the Ze reading at the incoming supply. All normal for a TNC-S it was about 0.14 ohms. I installed a socket in his workshop recently and as his tenant was in i could not remove the main earth so i took a Zs at the same position. The Zs reading came out at 0.01 ohms (the property is right next to the sub station) My issue now is that with a Zs so low it is giving me a PFC of over 14.5kA. I looked into replacing the MCB's for D-Type. Most of the values of circuit Zs are ok but a couple are higher than the stated regs. Although these are covered by a 30mA RCD, there are a few RCBO's in there which are not available as a typr D to withstand that potential in rush in the case of a fault. I also cannot find any literature on the fault rating of the main switch and RCD's in the board too. The make is M2 (CEF) I have called my registered body and they cannot suggest anything, i thought about putting some sort of resistor in line with the structural steel bond (which is the one causing this headache i believe) but i am not sure on the regs for doing that. It just seems all wrong! Has anyone come across this before and does anyone else test both Ze and Zs at the main board? I was only ever taught to take a Ze as required by the certs but i will take both from now on!
Thanks in advance.
Dave.