Probably a basic question
In an installation with pipework or cable ladder that's not extraneous as such but is connected to earthed metal
What's the logic for not main bonding it as the metalwork can surely introduce a potential in a fault situation?
The earthed metal would surely be bonded if extraneous, no?
It's either extraneous or it isn't.
Have you measured it ?
By earthed metal, I assume you mean metal that is connected to the MET?
For example: plastic incoming supply pipework, metal pipework to boiler, boiler connected to MET via CPC.
The metal pipework is not an extraneous part, so not introducing an extraneous potential. It is however connected to the MET via the boiler and CPC. All that bonding would do is connect it to the MET again, achieving the same thing.
Will it achieve the same result in the event of a fault?
The CPC connected to boiler or a main vond connected to the metalwork that's not extraneous
If metalwork is directly connected to earthed metal, what would be the point?
Am I missing something, here?
I believe so. Here's how I see it:
When a direct short occurs between L and earthed metalwork, a circuit is completed via the CPC, back to the MET, and back to the transformer via whatever earthing system is in place, and possibly through bonded extraneous parts.
Like any circuit, there will be voltage drop throughout the fault loop, with the highest potential for accessible metalwork being at the site of the fault, and the lowest being at the MET.
In my example above, the metal pipework is already connected to the MET via the boiler CPC, and is not taking a potential from anywhere else (it's not an extraneous part), so it can't be at a lower potential than the MET. Connecting the pipework back to the MET with bonding would not bring the potential of the pipework any higher than it already is.
Reply to Main bonding questions in the UK Electrical Forum area at ElectriciansForums.net
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
I'm probably displaying my ignorance here, but fortunately I'm not one of those people who can't stand to be laughed at! I've been thinking a bit...
I’m not working on this… not yet anyway, but can someone tell me why there’s a fuse or a link on the earth here? The green wire is bonded to...
This question has probably been asked several time but things change. The house I'm living in now was built in the 1960's and has a ring main...
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...