Jun 25, 2021
1,213
732
688
Ireland
Ireland
Probably a basic question
In an installation with pipework or cable ladder that's not extraneous as such but is connected to earthed metal
What's the logic for not main bonding it as the metalwork can surely introduce a potential in a fault situation?
The earthed metal would surely be bonded if extraneous, no?
It's either extraneous or it isn't.
Have you measured it ?
By earthed metal, I assume you mean metal that is connected to the MET?
For example: plastic incoming supply pipework, metal pipework to boiler, boiler connected to MET via CPC.
The metal pipework is not an extraneous part, so not introducing an extraneous potential. It is however connected to the MET via the boiler and CPC. All that bonding would do is connect it to the MET again, achieving the same thing.
Reactions: mainline
Yes I mean incidentally earthed via exposed metal
Will it achieve the same result in the event of a fault?
The CPC connected to boiler or a main vond connected to the metalwork that's not extraneous
I always found this article helpful, with regards cable tray;
Reactions: DPG and loz2754
If metalwork is directly connected to earthed metal, what would be the point?
Am I missing something, here?
I'll say the same as I did in #3
Without an actual measurement, we don't know if it's extraneous or not.
I believe so. Here's how I see it:
When a direct short occurs between L and earthed metalwork, a circuit is completed via the CPC, back to the MET, and back to the transformer via whatever earthing system is in place, and possibly through bonded extraneous parts.
Like any circuit, there will be voltage drop throughout the fault loop, with the highest potential for accessible metalwork being at the site of the fault, and the lowest being at the MET.
In my example above, the metal pipework is already connected to the MET via the boiler CPC, and is not taking a potential from anywhere else (it's not an extraneous part), so it can't be at a lower potential than the MET. Connecting the pipework back to the MET with bonding would not bring the potential of the pipework any higher than it already is.
Reactions: timhoward and ipf
I'm just presuming 'earthed metal' to be part of the earthing system. If something needs bonding, it's not.
I don't really know if they meant earthed as in to the Met or Earthed as in Terra Firma, which is why I asked the question.
Yeah, plenty of folk don't know the difference between earthing and bonding, though.
Not extraneous
I'm just trying to understand the shock risk between the pipework that is earthed by the boiler and another piece of exposed metal if it becomes live temporarily
So you've got 1 hand on the pipework and another on say a piece of live exposed metal
If you have one hand on a live piece of metal and another on a pipe that's earthed via the boiler, then you're going to get one of the worst types of shock you can have, one that's across your chest.
Ireland
Ireland
Main bonding questions
Mikegh,
mainline,