Black rubber flex is suitable for outside use Vitesse. H05RN or H07RN is what I have use, although I can't really see anything wrong with using H05RR either. I'd be doing the same, SWA along the run, into a suitable IP rated junction box and the black rubber flex into light from the JB.

Have you checked the voltage drop and expected Zs for this length of run? At a guess I'd think 1.5mm would be OK but I'd certainly do the calculations first. What is the total wattage of the lights?

Regarding H055RR my local supplier has H055RR-F available for a decent price. I know you said it should be ok. But specs say it shouldn't be used for long term outside use. I assume they are referring to it being used as a trailing flex? Do you reckon it will be ok clipped up a fence post for about 1.5 metres?

Regards
Tony
 
Regarding H055RR my local supplier has H055RR-F available for a decent price. I know you said it should be ok. But specs say it shouldn't be used for long term outside use. I assume they are referring to it being used as a trailing flex? Do you reckon it will be ok clipped up a fence post for about 1.5 metres?

Regards
Tony


Hi Tony,
I was taught in college that black rubber flex is ok to be used outside. Also, some members who are respected on this site are happy to use black rubber flex. I do realise that manufacturers instructions generally say to use H05RN-F if you are going to use it for continuous outdoor use and we do have to 'take account of MI's' as part of BS7671 (134.1.1), but we dont HAVE to follow the MI's to the letter if we deem our design to be safe and it adheres to BS7671.

I'm going off on a bit of a tangent! I would 'generally' be happy to use H05RR-F outside, however I cant actually see how or where you are going to install it. Fot instance I have used it at a stables and have then put it in conduit due to the nibbling mice. I have also decided on occasion to use H07RN-F as I want it to be a tougher for the environment. If it was going to be submerged in water then I would definitely use H05RN-F or H07RN-F, so only you can make the definite decision to use it.
 
Last edited:
On what technical information are you basing the advice the an RR cable can be used in place of an RN?
Do you know what the difference is and how that affects it's UV stability?
 
On what technical information are you basing the advice the an RR cable can be used in place of an RN?
Do you know what the difference is and how that affects it's UV stability?

None.
Yes.
No.
 
Actually would be interested to hear about the neoprene?

Black... to help deal with the UV.
Rubber... doesn't become as dry/brittle as PVC in sun.
Neoprene... I Dont know... superior UV resistance qualities?

Also you've mentioned TRS in post 10. TRS can be H05RR so would you use it?
 
As a general thing for black cables part of the black can be generated through the use of carbon black, this provides a good deal of UV resistance over a long period, however it does depend on how much the manufacturers put into the sheath; there is a minimum.
Neoprene (chloroprene) is more water resistant than ethylene propylene rubber and so will not suffer from water ingress.
TRS is a bit too general a term to be specific.
BS7671 goes on and on about H07RNF being suitable for various applications but no mention of light duty rubber cable..
Certainly HO5RRF is not at all suitable for situations where it may be exposed to heavy abrasion.
 