Discuss Manufacturer recommends 32amp breaker for 2kw appliance? in the UK Electrical Forum area at ElectriciansForums.net

stokielee

Trainee
Reaction score
12
Got to a customers house today after a brief discussion recently that they have brought a 2kw hob and it needs fittings. I went through the manufacturer’s instructions and they recommend it to be hard wired and that it is to be put on a 32amp breaker, obviously a 2kw appliance will pull around 8amps if my maths is correct so I am wondering am I missing something here? The hard wired part isn’t a problem, it’s more the size of breaker they recommend. There was 2x line and 2x neutral conductors too crimped together (this is where I first thought things weren’t what I am used to)
 

Attachments

  • 4D52FC67-207A-4FBE-9E49-0DAC27F13507.jpeg
    390.1 KB · Views: 68
Are you sure it’s only 2kw in total?
 
Can we have the model number of the appliance?

A lot of these are marketed for other countries as well as UK, where they have differing electrical supplies.
The MI can be misleading at times when things are written for one country, then badly translated.
 
Is this a single ring hob, or otherwise smaller than usual appliance?

If it is a normal sized hob with 4(or more) rings then it's more likely the error is in the 2kW rating and not in the requirement for a 32A supply.
 
Sounds like this was designed for a European setup, where it would have been provided with a different cable that split maybe 1/2 the rings onto each of the L and N.

In which case 2kW for half of the rings sounds more plausible. Or possibly someone has misunderstood our regs about any fixed load with >2kW needing it's only circuit.

There certainly are hobs that are limited in output power by their control circuitry to never exceed a maximum power, but they usually come with a plug attached.

Unfortunately, Manufacturers Instructions do have weight in the regs, even when they are badly written or just plain wrong.

I'd probably consider the 32A requirement to be more binding than the stated power output in this case. What is there already? If it's replacing an existing hob then what is there is probably suitable.
 
Got to a customers house today after a brief discussion recently that they have brought a 2kw hob and it needs fittings. I went through the manufacturer’s instructions and they recommend it to be hard wired and that it is to be put on a 32amp breaker, obviously a 2kw appliance will pull around 8amps if my maths is correct so I am wondering am I missing something here? The hard wired part isn’t a problem, it’s more the size of breaker they recommend. There was 2x line and 2x neutral conductors too crimped together (this is where I first thought things weren’t what I am used to)
32 amp breaker will be fine as the load is going to be no more than 2kw.
 
Can we have the model number of the appliance?

A lot of these are marketed for other countries as well as UK, where they have differing electrical supplies.
The MI can be misleading at times when things are written for one country, then badly translated.
I am just waiting on confirmation from the customer that they brought the hob that they originally sent me for approval
Sounds like this was designed for a European setup, where it would have been provided with a different cable that split maybe 1/2 the rings onto each of the L and N.

In which case 2kW for half of the rings sounds more plausible. Or possibly someone has misunderstood our regs about any fixed load with >2kW needing it's only circuit.

There certainly are hobs that are limited in output power by their control circuitry to never exceed a maximum power, but they usually come with a plug attached.

Unfortunately, Manufacturers Instructions do have weight in the regs, even when they are badly written or just plain wrong.

I'd probably consider the 32A requirement to be more binding than the stated power output in this case. What is there already? If it's replacing an existing hob then what is there is probably suitable.
There was nothing there, I have managed to feed a 6mm cable in on a 32amp breaker as recommended
Whatever it says (which is likely wrong) I'd never fit less than 6 sq mm cable for a hob supply anyway as who knows what someone will want in the future. So it might be simplest to go belt and braces and feed from 32A breaker and at least 6 sq mm cable.
That’s what I have done in the end, it was just the 5 core and the 2kw that has thrown me out a little bit
32 amp breaker will be fine as the load is going to be no more than 2kw.
Of course, a fixed appliance should never pull more then it’s max load but why recommend a 32amp breaker for 2kw in the first place
 
Of course, a fixed appliance should never pull more then it’s max load but why recommend a 32amp breaker for 2kw in the first place
I can only guess at the reasoning as to why, maybe they do different power ratings but stick to the same cable/mcb.
 
as
The 5 core flex indicates that this was designed to be connected to a 3 phase supply, but has been modified for the UK market. It's most likely 2kW per phase, so 4kW in total.
The doubled up 5 core flex is a better idea than the usual of brass links and then trying to fit 4mm2 cable to terminals designed for 1.5mm2.
Thank you, it’s starting to make sense now
 
I agree that the 2kW is probably wrong, it simply isn't enough power for a normal, full-spec hob, Nor would 2kW require the two pairs of L&N terminals. As @brianmoooore explains, many European 3-phase domestic systems use two phases for the hob, typically limited to 16A each. But I don't think they would normally quote power per phase, so it's anybody's guess where the supposed 2kW rating came from.
 
Right, things make even more sense today, the customer never brought the original hob that they sent me, they’ve got a completely different one and never told me.
I have attached photos of before and after.
Then, looking further into the operating instructions, each hob is 1200-2000watt so that explains the bigger cable/MCB now.
Sorry to waste your times, I shouldn’t of listened to the customer and double checked the instructions when the actual appliance arrived, I’ll put it down as a lesson learnt.
Thank you for all your comments and help.
 

Attachments

  • F98BB62A-DFA1-43CC-8E27-DD91A17F16AD.jpeg
    536.8 KB · Views: 34
  • 7A243C24-6555-4214-B39E-DCBCCFBF11C3.jpeg
    462.3 KB · Views: 34
The first picture says it has a 13A plug.
sureley it is limiting its current draw to less than 3kw in total.
 
The first picture says it has a 13A plug.
sureley it is limiting its current draw to less than 3kw in total.
The 13amp plug is what the customer originally sent me for approval then without telling me they have brought a different hob. Then I saw 2000watt on the box and assumed it was the original hob and required 8amps or there about.
 

Reply to Manufacturer recommends 32amp breaker for 2kw appliance? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all Some advice on this would be great. Due to wire a kitchen from scratch and in a pickle over the designing of the oven and hob circuits due...
Replies
6
Views
2K
Once again I am using the Engineering chat as I think my question is more theoretical rather than 'diy advice'. If I am misusing the forum...
Replies
17
Views
2K
The never ending debate about supplies for cooking appliances. ??? I've just received an email from a customer that I'm in the process of quoting...
Replies
14
Views
3K
I am at a standstill installing the new cooktop until I can determine if the new one works with the present wiring/breaker. (I am keeping in mind...
Replies
7
Views
1K
I have been inspecting and testing for some years and have until now believed that I have been doing it correctly. I spent some time at a property...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock