Discuss Max Zs on certification in the UK Electrical Forum area at ElectriciansForums.net

Dan007

-
Reaction score
8
Please can people clarify what value they insert in the Max Zs field on certification.

I've always input 100%. Currently in disagreement with another person as they are specifying 80%.

Done my 2391 in 2008 and I was taught and told it's always 100% and it's down to the QS to interpret the results and ensure they fall with 80% allowing for correction factors.

Third argument is that in GN3 and OSG they specifically state 80% - however I always understood these to be quick reference pocket guides while on site.

In the mentioned publications and BBB the model forms show 100% in the compelte fields for examples. Secondly the small print at the bottom makes reference to the Publication and values in Chapter 41 aka BBB and 100% values.

Your thoughts please people
 
The purpose of a well designed form is to make sure you only have to think about one thing at a time.
Therefore when filling it in you should do the full calculation, and when measuring the zs all you do is measure and fill in. Then to determine compliance you just compare the two without any other thought.
If part of the calculation is mixed with the comparison things would get very hairy.
 
New posts

Reply to Max Zs on certification in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Following on from another thread on here, can you please help me with a fundamental issue regarding certification bodies. Bear in mind we are new...
Replies
11
Views
2K
Hi all. I am collecting evidence for a report on the current 'strategy' and trust given to the competent person schemes by the Communities and...
Replies
13
Views
2K
D
Hi I was wondering if anyone could fill me in here. I tested an installation for someone which consisted of 2 circuits to a loft conversion I...
Replies
4
Views
938
NJG28
N
Hi guys i know this has been done do death, i have searched but i've not been able to find an answer. I'm having a mental block so just thought...
Replies
5
Views
2K
Hi guys, im new to this forum so go easy please ;) I am 17Th Ed and Part P Accredited. Have been doing electrical work for years ( commercial...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock