You have a distribution circuit protected by a 16A BS88 fuse on a TT system so your disconnection time is one second.
The time current characteristic tables in APP3 of BGB (p300) show a table in the top right for disconnection currents for various times.
From the table a BS88-2 16A with 1s Disconnection time has a minimum current required to trip of 75A.
230V / 75A = 3.1 ohms
So max Zs of dist circuit is 3.1 ohms at 70ºC
(In BRB p248 and 72A)