I'm installing a new supply to a ceremoniously dumped welfare cabin. I can't see any legitimate reason not to apply section 717, welfare units are specifically mentioned and the thing is a mobile/transportable unit. In turn this dictates that it shouldn't be connected to a TN earth as to my thinking at least none of the exceptions apply. Any arguments countering this are welcome!
So my current plan is TN up to a box near it, then become TT.
My question is about possibly using earth tape (I've never used it). As there's a nice 2.5ft deep 10ft long trench in preparation for a drain I thought it might make sense to use earth tape instead of banging rod(s) in.
I believe that I've calculated that 3m of tape, 0.75m down, with soil resistivity at an arbitrary worst case 150ohm-meters should give me 35 ohms impedance. As I can see clay I think this is a reasonable worst case guess.
Any superior wisdom welcomed, I'm really seeking confirmation that it's likely I can get a better result far more easily with tape in this case.
Earth tape is a good idea, even adequate size of bare copper wire would be good and might be easier to bring out and/or crimp join to an insulated./sheathed conductor to the cabin. A trench 2.5 feet down ought to avoid frosting and any major risk of drying out.
Consider condu-disc and condu-crete.
Thanks .....but I already have!
In this case I'm not sure it's the obvious choice as there is already a nice big long deep trench. The internet is silent about the actual cost of them, and anything you have to ask the price of is usually liable to require a stiff drink afterwards to recover.
Thanks all
Thanks for the idea. The earth tape I was looking at was 25 x 3mm. Result should have in fact been 45 ohms. (area vs diameter mistake!)
If I bung in 16 sq mm bare copper that gives 47 ohms, and that is worst case for soil conditions. If I add a rod for good measure I think this idea should be fine.
I'll report back on the final impedance result!
It is quite surprising how you can never find the price for some these pieces of kit and that also casts doubt on the availability
I am always suspicious of products that are not quoted (unless obvious issue like custom build) as experience has taught me it means "stupidly expensive, but now we will pester you with sales calls".
The Conducrete looks useful, but it appears to be extremely difficult to get hold of. Why is this product not readily available at electrical wholesalers?
Reply to Maybe use copper Earth tape? in the UK Electrical Forum area at ElectriciansForums.net
Hi all, For clarity, I'm not a qualified electrician, but have a reasonable amount of experience as I've done plenty of wiring (signed off by a...
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Correctly closing off a dead twin and earth cable in a loft. My old house used to have radial circuits serving night storage heaters. Those...
  • Locked
5K