sinse when has max VD been 12V...
Risteard: Another Sparky mentioned it to me and said that the breakers in the new DB should be lower that the supply feed to avoid nuisance tripping.
Shocking_eg: Sorry I should have mention that the current supply is TT so yes the supply in the workshop will also be TT.
Lighting Vd is 3% of 230v= 6.9v and power is 5% of 230v=11.5v so your way over if lighting is involved which as its a workshop i presume it is


and so it will be everywhere else n all....Thanks for all the input guys!
The supply voltage where I live is actually 240v, so my volt drop complies with the regs. The only light that will be used will be at the most 4 twin flourscents. I would like to say that no other circuits will be added such as heaters etc as I am telling the customer that the cable will not be suitable for more demand.
The reason for not connecting the MET of the house to the MET of the workshop is due to reading the attached article from the NICEIC Connections magazine.
View attachment 19145View attachment 19146
I love it !!Thanks for all the input guys!
The supply voltage where I live is actually 240v, so my volt drop complies with the regs. The only light that will be used will be at the most 4 twin flourscents. I would like to say that no other circuits will be added such as heaters etc as I am telling the customer that the cable will not be suitable for more demand.
The reason for not connecting the MET of the house to the MET of the workshop is due to reading the attached article from the NICEIC Connections magazine.
View attachment 19145View attachment 19146
=Squid_uk;781182]Thanks for all the input guys!
The supply voltage where I live is actually 240v, so my volt drop complies with the regs. The only light that will be used will be at the most 4 twin flourscents. I would like to say that no other circuits will be added such as heaters etc as I am telling the customer that the cable will not be suitable for more demand.
The reason for not connecting the MET of the house to the MET of the workshop is due to reading the attached article from the NICEIC Connections magazine.
View attachment 19145View attachment 19146
You'll have to enlighten me as to what is wrong with interconnecting the MET with the EMT on an all TT installation??
542.1.8 states...."where a number of installations have separate earthing arrangements...."
well, if the MET and EMT are joined by a common conductor thay are not separate are they?
What the hell would it matter, when both the house and the outbuilding earthing system is TT??