Ok, I'm prepared to be shot down in flames for this, but one or two recent threads have made me think:

Senario: 32A MCB changed to 32A RCBO in preparation for new shower (instructions and plumber have asked for change).

I say not notifiable on the basis that the value of the OCPD is unaltered:

The circuits protective measures are unaffected


Your thoughts?
 
i would say that as you're adding RCD protection to the circuit, it's notifiable, but having said that, i for one , would not bother.
 
I say not notifiable on the basis that the value of the OCPD is unaltered:

The circuits protective measures are unaffected

The protective measures are affected, they're improved!

But, if you're changing the device, I guess you're also certifying that the new device is suitably rated for the cable and load. ie, if you found the circuit wired in 2.5mm², you wouldn't just fit an RCBO and walk away.
 
Not notifiable if shower is like-for-like. You have neither added a circuit, nor changed protection characteristscs.
Personally I would fill out an MWC recording new RCD readings.
 
Strictly speaking you have made an alteration to a circuit by changing the device that protects it. If you change a fuseboard it is notifiable with an EIC required. So surely this falls under the same bracket but on a smaller scale. One circuit instead of the whole board therefore using a MEIC should be the way to go. Be interesting to see how many actually do do the paperwork for a 10 minute job.
 