Quick Question. Despite being 50 I am a newbie electrical installer. Preparing for my retirement from public service. Anyways - my Question. How the hell do MCBs work on a TT system. Say Ze is 33 Ohms with a 240 supply the PFC will be just over 7 Amps. How does that trip MCBs or is there were the importance of RCDs come in. Can someone explain??
 
In many instances ADS wont be achieved and must be satisfied by other means.

I don't mean to seem disrespectful (especially as I'm an apprentice only a few years younger than you), but this should have been covered at length when you were training.
 
You need to study the curve and in most cases a very low fault current won't trip an mcb , maybe a 6amp but not much else certainly not fast enough to achieve ADS

This is why TT installs had upfront RCDs Or Voltage operated earth leakage devices or what ever they were called back in the olden times
 
In many instances ADS wont be achieved and must be satisfied by other means.

I don't mean to seem disrespectful (especially as I'm an apprentice only a few years younger than you), but this should have been covered at length when you were training.
Thanks. 28 years ago I sparked but on aircraft. Avionics to be specific. Have HNC in EE. My DEI course was basic and in no way do I see myself as a Electrician. Yea we covered the OSG in alot of detail and there was nothing about TT values apart from needs to be under 200 ohms Ze. I suppose I get credit for coming up with the question. Like you and (prob more than you)I have alot to learn 😆
 
The best of us admit that we ARE ALWAYS LEARNING.

I have only ever met a couple of sparks who were sure they knew it all.
strangely enough I didn’t get on with either of them very well.😆😆😆
 
Thanks. 28 years ago I sparked but on aircraft. Avionics to be specific. Have HNC in EE. My DEI course was basic and in no way do I see myself as a Electrician. Yea we covered the OSG in alot of detail and there was nothing about TT values apart from needs to be under 200 ohms Ze. I suppose I get credit for coming up with the question. Like you and (prob more than you)I have alot to learn 😆
The best of us admit that we ARE ALWAYS LEARNING.

I have only ever met a couple of sparks who were sure they knew it all.
strangely enough I didn’t get on with either of them very well.😆😆😆
On that basis James we’ll get on like a house on fire 😂
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Northern Ireland
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
MCBs ADS in TT system
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
9

Thread Tags

Advert

Thread statistics

Created
Jonny72,
Last reply from
westward10,
Replies
9
Views
3,765

Advert

Back
Top