Hi all,i have recently purchased a megger 1553 mft & because i'm new to the game i was having a play with it & reading the user manual & just wondered what the function for the RCD touch voltage selection would be used for could anyone give me an example.You can select from 25v - 50v.this may be an easy question to most of you so go easy on me,because as i go along i will be asking more of the same questions:D
 
i think its for agricultural installations but im sure someone will confirm or correct me:)
 
Hi

The 50 volt touch is for non hazardous locations and the 25 volt touch voltage is for agricultural, horticultural and construction sites under 16th Edition

Regards

Megger Technical Support
 