AFAIK, capping isn't a regulation in the 17th edition although if you want to avoid having to protect a circuit with an RCD or RCBO then ALL cabling on that circuit MUST be buried at least 50mm into a wall (as long as that doesnt take it to within 50mm of the other side of course!) OR must be capped with earthed metal capping.
hat's how I understand it anyway or have I mis-understood your question.
Oh, and as for earthing the capping, it's so that if you nail through the capping and into the live without making contact with the cpc then the fault is grounded by the capping.