We have had 2 metal steps installed to cover main supply cables (out to flats) from a Ryefield .
when measured IR from MET to steps i got 0.091 MegOhms.

The usual calculations are for when a 30 ma RCD is protecting (which is not the case here)

91 Kohm is above the usual value of 23 Kohm I usually use (10ma).

Should these be bonded to earth?
 
I wouldn't earth it. As you say using the equations the maximum current that flows through the body is < than 10mA.

Using the formula from GN8:

1637827866097.png

rearranged to:
1637829024815.png


I get 2.5mA when taking ZT as 1000ohms as suggested in the guidance.

Are there any other earthed parts within touching distance? GN 8 states "Consequently, for a conductive part to be able to introduce a potential to a person (or livestock) in contact with the potential of any of the conductive parts, that part should be accessible to such a person (or livestock)." I assume this would also apply to your situation.

(I am referencing the 17th ed amd 2 of guidance note 8)
 
  • Like
Reactions: loz2754
Yes there is a metal ryefield on the PME earth and a 3 phase DB easily touchable
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

newfutile

Arms
Supporter
~
Joined
Location
hemel hempstead
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Metal steps secured to concrete (bonding)
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
newfutile,
Last reply from
newfutile,
Replies
2
Views
1,230

Advert