We have had 2 metal steps installed to cover main supply cables (out to flats) from a Ryefield .
when measured IR from MET to steps i got 0.091 MegOhms.

The usual calculations are for when a 30 ma RCD is protecting (which is not the case here)

91 Kohm is above the usual value of 23 Kohm I usually use (10ma).

Should these be bonded to earth?
 
I wouldn't earth it. As you say using the equations the maximum current that flows through the body is < than 10mA.

Using the formula from GN8:

Metal steps secured to concrete (bonding) 1637827866097 - EletriciansForums.net
rearranged to:
Metal steps secured to concrete (bonding) 1637829024815 - EletriciansForums.net

I get 2.5mA when taking ZT as 1000ohms as suggested in the guidance.

Are there any other earthed parts within touching distance? GN 8 states "Consequently, for a conductive part to be able to introduce a potential to a person (or livestock) in contact with the potential of any of the conductive parts, that part should be accessible to such a person (or livestock)." I assume this would also apply to your situation.

(I am referencing the 17th ed amd 2 of guidance note 8)
 

Reply to Metal steps secured to concrete (bonding) in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock