Yes, still doubting my own judgement when it comes to supp bonding and EICRs, so would welcome any thoughts on the latest one.

Newish flat (2000s) with MK split board, so no RCD on lighting.

Bathroom contains:

Vent cap only (some clever full flat extraction system that isn't currently working, but that's another issue...)
Plastic shaver socket, with plastic back box, so no parts that could reasonably be expected to become live
SELV downlights, with fixed brackets above on inspection, so no earthing of front plate
Metal Towel radiator, but plumbing in plastic microbore pipework so nothing to bond.

So in summary, no extraneous-conductive parts that could be tested for effective bonding back to the MET.

From an inspection of the shaver socket, no supplementary bonding conductor is in place, but as stated it contains no extraneous-conductive parts.

the ESF best practise guide states not to code absence of supplementary bonding for installed Class 2 equipment, but that isn't quite the circumstance here, though there are similarities in the fittings not requiring an earth on the load side for protection.

I'm currently on a C3 for this, but any opinions welcomed. If there were extraneous-conductive parts I'd be a C2.

Since I'm going back and this is a regular landlord I may suggest fitting an RCBO on the lighting circuit in question anyway, just to be sure, since it covers a main bathroom and an en suite.
 
Are taps etc supplied by plastic pipes?
Good question. It was a pedestal sink type where the pipes weren't immediately accessible, and similar under bath so can't be sure, but I suspect plastic - the main building incoming was in steel or coated copper to the boiler, but after that all the central heating is in plastic and I think water too...
 
Good question. It was a pedestal sink type where the pipes weren't immediately accessible, and similar under bath so can't be sure, but I suspect plastic - the main building incoming was in steel or coated copper to the boiler, but after that all the central heating is in plastic and I think water too...
Assuming plastic pipes to the taps, I don't think sup bonding would be necessary here.

There are no extraneous parts, the OSG tells us no need to bond metal supplied by plastic pipes (4.8). I assume the shaver and lights are on the same circuit, so CPCs are connected anyway, but even if they weren't, the lighting is ELV so not subject to ADS requirements.

No code for me
 
Assuming plastic pipes to the taps, I don't think sup bonding would be necessary here.

There are no extraneous parts, the OSG tells us no need to bond metal supplied by plastic pipes (4.8). I assume the shaver and lights are on the same circuit, so CPCs are connected anyway, but even if they weren't, the lighting is ELV so not subject to ADS requirements.

No code for me
That makes sense, thanks - though I will probably make a comment just to show that I've considered it.

Will probably recommend an RCBO on that circuit anyway, since I have one in stock...
 
Is there any continuity between the bathroom circuits ?
Is there an electric shower?

If there is only a lighting circuit and the screw on the shaver socket is on the lights then I would think C3

Have you done the R2 then IR test to confirm either below 0.05 ohms continuity or over 200M IR ?
 
Is there any continuity between the bathroom circuits ?
Is there an electric shower?

If there is only a lighting circuit and the screw on the shaver socket is on the lights then I would think C3

Have you done the R2 then IR test to confirm either below 0.05 ohms continuity or over 200M IR ?
No electric shower - and really nothing I could test between electrically without significant disruption to decor, which wasn't an option under the limitations agreed (after 4pm, client working from home, etc)

The shaver socket was on the lighting circuit, but plasterboard back box, so screws not connected to earth. The lighting is SELV MR16 lamps and therefore no earthed fronts to the lights. I didn't investigate too far into the ceiling to avoid damaging decor as they were in tight, but from what I could see installed well. Towel rail supplied by plastic microbore piping, as were all the radiators.

I did R2 with a wander lead as part of inspection and got no continuity to anything in the bathroom, but that is what would be expected with the setup as it was. The only thing I may have missed was an R2 to the taps, but the main water bond was in place and effective.
 

Reply to Supp bonding requirement with no extraneous-conductive parts? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Just had my design project handed back to me from my last block and I got everything right apart from one question Q9 I would take a photo but...
Replies
3
Views
1K
in the old bpg4 it stated Absence of supplementary bonding for installed Class II equipment where required (such as in a location containing a...
Replies
1
Views
1K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Good morning everyone. I’m looking at getting an EV charger installed at my home and the company is requesting that I earth bond my water supply...
Replies
8
Views
4K
Yes, it's another EICR coding question - hurrah! :blush: Inspecting a small 1 bed 70s ex-council flat that was going well. Main Bonding had...
Replies
12
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock