excellent, on closer inspection of the metering set up and supply tails i can confirm they are 16mm on a 80amp fuse with the cables clipped to the wall and enclosed in trunking (apart from where it disapears for about 50cm under plaster board and enters the back of the consumer unit..!!! shall i change tails to 25mm or leave 16mm!!
 
best check about the length of tails and the need of a switchfuse is over a certain length. 3m i think then you need one.

D.
 
iv recently bought a house.Fitted new db.However its about 7 metre run for the tails. it has a switch fuse at the 3m point inside a cupboard and then carried on the further 4 metres.Is this ok or have i been mis informed.
 
If it is a 100A fuse then the tails need to be 25mm, also if they are buried in the wall, not enclosed in metallic conduit, they will need RCD protection.

Can you run surface trunking to the DB??

Think your having a laugh about the RCD. Or are you serious?
 
Deadly......unprotected (i.e no armour or earthed metallic conduit), PVC PVC cables buried in the fabric of the building at less than 50mm....additional protection by RCD required.;)

This is why the IET ammendment to the 17th ed and the ridiculous "RCD everything" is on the way.
 
Deadly......unprotected (i.e no armour or earthed metallic conduit), PVC PVC cables buried in the fabric of the building at less than 50mm....additional protection by RCD required.;)

This is why the IET ammendment to the 17th ed and the ridiculous "RCD everything" is on the way.

I presume electricians houses to be exempt
 