OK, so in the onsite guide on a TN-C -S system, "Tails must be minimum of 25mm" ok fair enough, but how come on the suppliers side, they are always 16mm?? I went to a new install yesterday, all nice and tidy but 16mm tails used.
 
where in the osg does it say that. i use 25 anyway but just wondering and osg not near me. I assume it is incase the fuse is upgraded to 100A.
Also there is a article in the esc newsletters (i think at least) where they say 16mm is ok if the max demand, condition of cables and fuse size are compatible with 16mm.
 
BS 7671 only covers consumers installations, the DNO equipment is ESQCR 2002.
 
Yes I agree and have you seen the DNO cables to many large commercial installations?

You have a nice 185mm on the consumers side and this pathetic bootlace of a DNO cable enters the Bemco unit!
 
Yep DNO cables 16mm DI 6mm main earth Yet we put in 25mm DI and 16mm earth plus 10mm gas/water looks nice though
 