Hi
I recently visited a property the was experiencing tripping of an Mcb when turning on a 3 kw hand wash appliance in a down stairs loo.
All earth cables present and correct, old wired board but with plug in MCB's No Rcd protection.
Some Numpty had wired the hand wash to the 6 amp alarm and bell circuit with 1mm 3 core cable.
So the MCB was doing its Job.
So i ran 2.5 cable from hand wash unit back to the board to a little used 16amp MCb.
Problem solved. All tests fine and Zs 0.26.
So Minor works certificate ? Installation Certificate? and is it Notifiable?
Any response is greatly appreciated, Thanks.