Hi all,
I was at a property yesterday and found a number of problems with their installation.
To name a few.
6mm radial supplying a 8.5kW shower and 3.5kW emersion heater on a 32A RCBO.
Extractor fan unfused and spured from shower in 1.5mm cable.
Isolator and light switch in zone 2.
When we finished our work and tested loop impedance we had a result of 85 Ohms (water bond was in place). When investigating we found that there was no link between the main earth of the Tns system to the consumer unit. ( pictured top left incoming earth in Henley block)
We rectified the problem and had a loop impedance of 0.57 Ohms.
The reason for my post is, since finding this I have wondered if a board is not adequately earthed would this prevent an RCD from tripping? As in if the earth is not intact will it provide a path for fault current to flow and trip the RCD?
I have only just finished my first year of training and any advice would be greatly appreciated.
I was at a property yesterday and found a number of problems with their installation.
To name a few.
6mm radial supplying a 8.5kW shower and 3.5kW emersion heater on a 32A RCBO.
Extractor fan unfused and spured from shower in 1.5mm cable.
Isolator and light switch in zone 2.
When we finished our work and tested loop impedance we had a result of 85 Ohms (water bond was in place). When investigating we found that there was no link between the main earth of the Tns system to the consumer unit. ( pictured top left incoming earth in Henley block)
We rectified the problem and had a loop impedance of 0.57 Ohms.
The reason for my post is, since finding this I have wondered if a board is not adequately earthed would this prevent an RCD from tripping? As in if the earth is not intact will it provide a path for fault current to flow and trip the RCD?
I have only just finished my first year of training and any advice would be greatly appreciated.