Hi,
I am currently training to become an electrician. I have passed all relevant C&G level 2 exams along with C&G level 3 inspection and testing and principles of electrical science.
I have been asked to help design some garden circuits but been given specific instruction on how the circuits will be protected.
Could you please give me feedback on the attached plan.
Specific questions are ;
1) If the 4mm2 cores of the SWA have a current carrying capacity of 37A, can I use only 2 cores for my neutrals and 4 cores on separate circuits.
2) Are my earthing arrangements correct? i.e. 4mm2 through the house then using the SWA armour as the earth to the front gates.
I would be installing DBs in the shed and green house, supplied with 2 or 3 core SWA, and local RCD.
For the gates, again, probably be a local (to the gates) DB because you're going to require an enclosure to split your 7 core into the individual circuits anyway.
Whether I'd have the RCD there or back in the house, hmmm, depends on inconvenience level if it trips.
Each circuit must have its own seperate neutral, sharing a neutral between circuits is very dangerous for anyone working on these circuits in the future.
It is more of a parallel conductor design than being a shared neutral in my opinion. The person I am working for is electrically qualified and this is how he said we wire it. I am unsure that is the reason I am asking here.
In this configuration it is impossible to get a dangerous voltage on the neutral so long as the neutral is terminated in the consumer unit, same as any circuit. It is not like a situation when you borrow a neutral from a different lighting circuit. It is not a dangerous configuration.
Apart from the shared neutral being dangerous, which I do not think it is in this configuration, is there any reason why we could not wire it as shown?
If you don't think a neutral conductor shared between circuits is dangerous then maybe you should step away from this job.
I know of configurations in which sharing a neutral can result in a dangerous voltage on the neutral. I knew this thread would go down this path. I could draw the situation, can you? If so draw it then explain how the fault relates to this design.
You either need cables which incorporate more cores for individual neutral conductors or fit distribution boards at the areas the circuits are required.
Actually thinking about it, You are right. Exactly this situation could occur, you could leave a circuit powered then disconnect the neutral at the termination at the end of the SWA and the neutral from another circuit could become live. Sorry you are right. It could be dangerous. Thank you :)
I know I’m only a trainee but that design does look over complicated. DB at each location and 3 core SWA calculated on max demand and distance.
It is not a parallel conductor design, that would be a single circuit spread over multiple conductors.
The regulations prohibit the use of a shared neutral conductor in the manner you are suggesting.
It is dangerous, if someone was to isolate one of these supplies and disconnect the neutral at any point in the circuit where it may not be obvious what you have done the disconnected neutral will become live.
Any EICR carried out in the future will identify this as potentially dangerous and you could have a very angry customer coming back to you, taking legal action against you or generally ruining any good reputation you may have.
This plan is also a bad idea from a common sense point of view, any person working on the circuit in the future may need to isolate up to 5 circuits to carry out work on one of them safely . So you end up with a situation where you have to isolate an alarm and two gates to repair or extend an apparently unrelated lighting circuit.
It is over complicated, I would design it different, but the person who's house it is wants all the breakers in one location.
Good point, thank you. Glad I checked with the forum.
Do you know what reg, forbids shared neutrals?
Reply to Multi-core neutrals and earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hey, I have a shed in my garden that was built and wired up by my granddad a lonnng time ago and it currently uses 2 core/twin and earth cable...
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Hi, Currently undertaking an EICR on a factory, we have came across an 4 core SWA and 4 Core SY which have been split in the DB to serve two...
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...