I have a Fluke digital multimeter and whilst testing live to earth on a controller, it tripped the rcd.
Can anyone explain why?
Is it like the fluke t120 voltage indicators where you have to test between live and neutral for 5 secs beforehand?
Should be a low current test, if it is and its still tripping try reversing the polarity of the test, ie live down earth and earth down live, some of the new rcds have this problem and reversing the polarity seems to solve it, also make sure there are no loads on the circuit
i would hope that you were measuring voltage, not current. it would seem that the meter is drawing sufficient current to trip the RCD.
Can't believe a digital multimeter would draw enough current to trip an RCD, my money's on the 'using it as an ammeter' theory. Daz
When you say it has to be held on live to neutral for 5 seconds is that for the continuity buzzer to work. I had an alphatec that would trip rcds If you tested on live to earth before live to neutral as charging the internal capacitor that powered the buzzer drew enough current to trip most rcds. Useless it was and had a very short spell in my toolbox.
Yes my fluke multimeter 117 has LoZ function to prevent phantom voltages from being displayed, I think I might try it tomorrow to see if it trips the rcd on L-E test.
Reply to Multimeter tripping rcd... in the UK Electrical Forum area at ElectriciansForums.net
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Having a challenge understanding the concept behind why when you measure across line and neutral (live circuit) using voltage indicators we have...