I’m still an apprentice electrician so the whole thing around diversity is still a bit confusing to me

A family member has moved into a new flat. The existing cooker circuit is 6mm on a 32A MCB. She has bought a cooker which pulls 9.6Kw.

I know you do 9600/230 = 41.7

This is telling me that a 32A isn’t going to suffice for this, or am I wrong?

I am going to recommend to her that I rewire the cooker supply in 10mm and put it on a 40A MCB. Is this correct? If not, if someone could break it down to me how you work out the diversity it would be appreciated
 
Check out the manufacturers instructions for recommended supply.
 
Diversity can be applied to cookers as there on thermostats , once they reach the set temp they turn off until its cooler than set temp when they turn on.
Therefore we can apply diversity as follows: Cooking: 10A + 30% of cooker full load above 10A and + 5A if there is a cooker socket

10+(30% x 31.7) 9.5 = 19.5 amps +5 amps if you have a cooker socket =24.5 amps
 
It is probably OK as unlikely they would turn on everything at once. That 42A max on a 32A MCB would trip somewhere between around 1 and 10 minutes so there is a sporting chance that the thermostats would have started acting and reducing the average current to something closer to the diversity rating.
 
Last edited:

Reply to Need help with cable size and breaker size in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Replies
23
Views
954
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
725
I would like to reuse a 10mm cable to provide a ring circuit in an area. The cable is currently used for an electric shower, still connected at...
Replies
10
Views
387
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K
Came across a cooker circuit with 10mm and 40A rcbo. Last leg was 6mm. Isolator to outlet. I downgraded to rcbo to 32A to accommodate the 6mm...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock