I’m still an apprentice electrician so the whole thing around diversity is still a bit confusing to me

A family member has moved into a new flat. The existing cooker circuit is 6mm on a 32A MCB. She has bought a cooker which pulls 9.6Kw.

I know you do 9600/230 = 41.7

This is telling me that a 32A isn’t going to suffice for this, or am I wrong?

I am going to recommend to her that I rewire the cooker supply in 10mm and put it on a 40A MCB. Is this correct? If not, if someone could break it down to me how you work out the diversity it would be appreciated
 
Check out the manufacturers instructions for recommended supply.
 
  • Like
Reactions: Baddegg
Diversity can be applied to cookers as there on thermostats , once they reach the set temp they turn off until its cooler than set temp when they turn on.
Therefore we can apply diversity as follows: Cooking: 10A + 30% of cooker full load above 10A and + 5A if there is a cooker socket

10+(30% x 31.7) 9.5 = 19.5 amps +5 amps if you have a cooker socket =24.5 amps
 
It is probably OK as unlikely they would turn on everything at once. That 42A max on a 32A MCB would trip somewhere between around 1 and 10 minutes so there is a sporting chance that the thermostats would have started acting and reducing the average current to something closer to the diversity rating.
 
Last edited:

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Luton
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Need help with cable size and breaker size
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
Uplight99,
Last reply from
pc1966,
Replies
3
Views
1,518

Advert