Got a neutral to earth fault on a ring final which is tripping the RCD instantly when trying to reset.





Tested at the board and I’ve got continuity between neutral and CPC. Disconnected the ring and split it into two legs and identified the faulty side.





This only started happening after I installed a new cooker circuit, although I haven’t used any fixings that could have damaged cables. Not sure if that’s just a coincidence or related.





I’ve unplugged everything I can think of on the circuit so I don’t believe it’s appliance related.





Before I start lifting loads of sockets, has anyone got any quicker methods or tricks to pinpoint the fault with minimal disturbance?





Any advice appreciated.
 
The continuity reading should give you some idea of how far away it is. Plot out the faulty side using R1+R2 and draw it down on a plan then break that faulty side down say at halfway you should be able to locate it.
 
If it only started after 'installing a new cooker circuit' then that would be the first place to look!

Not entirely sure what you mean by 'installing a cooker circuit' onto a RFC?

Apologies, the cooker supply, is a dedicated circuit. Not connected to the RFC.

I left the job with everything in working order. After 30mins I received the dreaded phone call that the RCD has tripped and would not reset. Even with the MCBs in the off position.

The cooker supply is ‘free floating’ so i have not disturbed any fabric of the building as such. It’s a strange one!

I’ve disconnected the cooker supply entirely from the DB. Still getting a fault on the RFC between N+CPC.
 