soulman

Hi,


I have a job to connect up a Single phase sunbed in a salon. I have telephone the manufacturer for the spec of the sunbed. They have told me I must use the following; 63A type c circuit breaker, 10mm cable into 63a rotary isolator & the circuit is to be protected by a 100ma rcd. I have asked for these instruction to be e-mailed to me. They said they do not give out exact spec's as they have a problem with electricians quoting much higher starting currents. Also the 100ma rcd must be used & dont be tempted to put in a 30ma.

The DNO have installed a new meter especially for the sunbed. 100A fuse. TNCS

I intend to do the following; from suppliers isolator 25mm tails into an 80a switched fuse. Out of the switched fuse with 16mm 3 core swa for 16 meters to ccu. I will earth the armour & also use the 3[SUP]rd[/SUP] core as an earth. I have used 63a as design current, the cable will be clipped direct which gives me 77Amps & volt drop of 2.41v. (which I got from pages 334 & 335 of the brb). I will go from the consumer with 16mm T&E straight into a rotary isolator. Then connect to the bed.

Does the above sound o.k, have I missed anything.

I am also concerned about the eli value for a 63 type c breaker 0.29ohms.

Any help would be appreciated

Cheers
 
So, are you using a 100mA RCD as suggested, and keeping the T&E surface mounted/trunked?
 
Cheers Guitarist, Yes i will be using the 100ma rcd. The T&E will be less than 20cm straight into isolator. I have also had it pointed out to me, that the cable will need to be 25mm from the switched fuse to the consumer.
 
I'd use a Garage unit with the RCD and 63A breaker housed in it then run the swa to the isolator, aesthetics ‎pending

& also use the 3[SUP]rd[/SUP] core as an earth

Have not got the book with me to double check it but probably wouldn't bother with that
 
I'd use a Garage unit with the RCD and 63A breaker housed in it then run the swa to the isolator, aesthetics ‎pending



Have not got the book with me to double check it but probably wouldn't bother with that


Aye up Finn

but it will help pull down the Zs for the type C....?

- - - Updated - - -

Ohhh yes member of the 3000 club. Wheres the red carpet
 
Hi the metering equipment is outside, that's why i was putting in the switch fuse to protect tails. The consumer will be 16 metres away.
 
All this for a single sun bed!! I hope they can make some money out of it, after paying for the leccy bill? ...lol!!
 
Hi, can anyone confirm for me that op is o.k I will still use 16mm swa, I will use the thermosetting which take about 94a. Cheers
 
Hi, can anyone confirm for me that op is o.k I will still use 16mm swa, I will use the thermosetting which take about 94a. Cheers


don't forget, if the switches etc. connected to that cable are only rated at 70deg. then you need to rate the cable at 70deg.
 