Colin33

-
Arms
Reaction score
69
I've been asked to do some work on a domestic installation. However, it seems all but the shower and garage supply are not RCD protected. Does anyone know if single module rcbo's are available for this Merlin Gerin board or is it gonna have to be changed?

New Consumer Unit Needed? IMG_20171016_091843 - EletriciansForums.net
 
Look for Schneider C60H RCBO.

Seems to be a lot of C curve MCBs in there for a domestic board.
 
Look for Schneider C60H RCBO.

Seems to be a lot of C curve MCBs in there for a domestic board.
I could only find Schneider ones which don't look like they'll fit (wrong way up) Yes they're C types, think who ever did this was probably more accustomed to industrial work. A metal Cu in a domestic premises before AM3?? Whatever next?
 
You will get Schneider ones to fit that just say they are for a Merlin Multi 9 board.
 
Try and get the Schneider C60H range, the iC60H will fit but not perfectly as they are slightly narrower and a bit taller.

What is wrong with a Type C in a domestic.

Absolutely nothing as long as the disconnection times are met and fault current is sufficient to trip them. I'd much prefer to work on that board than some of the modern options available.
 
Thanks for your help guys. A quick google and 6 of these RCBO's will cost around £216, which is about what a new loaded CU with 8 rcbo's would cost. But labour will be a lot less of course...
 
Why does the garage need RCD protection and why do you need 6 RCBOs?
No idea why the garage has an RCD at this end, but it can stay put. I would replace the 6 mcb's in use with rcbos. Only need to work on /add to two circuits but why not do the job properly and make sure all circuits are protected?
 
Sorry misunderstood, thought you were saying the shower and garage needed RCD protection.
So your intention is to upgrade the installation to the 17th?
 
No idea why the garage has an RCD at this end, but it can stay put. I would replace the 6 mcb's in use with rcbos. Only need to work on /add to two circuits but why not do the job properly and make sure all circuits are protected?
There is no requirement to add additional rcd protection to circuits you are not working on.
 
Sorry misunderstood, thought you were saying the shower and garage needed RCD protection.
So your intention is to upgrade the installation to the 17th?
I have to add some sockets and lights, so certainly want to make sure all is rcd protected. As for upgrading the whole installation, it's mainly old coloured wiring and probably missing a cpc on some of the lighting circuits too but a rewire is not an option at this time...
 

Reply to New Consumer Unit Needed? in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock