R
rajshar
Thanks Strima.
The suppliers installer will fit the correct cables if he deemed necessary. between meter and isolator and between cutout and meter as anything after cutout to meter is the suppliers responsibility.
Now I could be completely wrong but isn't that with a 100 amp fuse the 16mm tails aren't suitable as they have maximum rating of 80amp. We had smart meter fitted April 2020. I am just wandering that why they didn't upgrade the right tails or downgrade the cut out fuse that time. That time I knew nothing about any standards or regulation otherwise I would have asked the installer for this and would have arranged for an isolator at the same time.
The other issue is the earth cable. Now we don't have the earth conductor or earth block. The earth cable goes direct to the fuse board from cut out. The current earth cable doesn't comply even with 16mm tails. I believe it should be 10mm in the current settings and if upgrading to 25mm cable it should be 16mm. Even this wasn't pointed out to us by the meter installer. May be it's not their job to change the cables but at least during the installation, they should be inspecting that equipment is in compliance. Or is it that my equipment is still in compliance because new regs don't apply retrospectively. Anyway when suppliers installer comes to fit isolator and decides that 16mn tails are good enough, shouldn't then who ever is responsible, change the cut out fuse to the correct rating. Although upgrading the tails should be the best option.
Now some electricians have no problem to upgrade the earth cable and some just getting out of it by saying they don't touch the cutout as this 2nd electrician said. It also makes me wonder that how he was going to change the CU without any isolation because he didn't knew that I had arranged for an isolator to be fitted. I think I should at least ask one more quote and see what he/she can or can't do.
All this brings up new questions. All the CUs come with 100 amp isolators. Do we still need an isolator inside the CU, if one fitted outside, if yes should it be lower rating than the 100amp?
Thanks.
The suppliers installer will fit the correct cables if he deemed necessary. between meter and isolator and between cutout and meter as anything after cutout to meter is the suppliers responsibility.
Now I could be completely wrong but isn't that with a 100 amp fuse the 16mm tails aren't suitable as they have maximum rating of 80amp. We had smart meter fitted April 2020. I am just wandering that why they didn't upgrade the right tails or downgrade the cut out fuse that time. That time I knew nothing about any standards or regulation otherwise I would have asked the installer for this and would have arranged for an isolator at the same time.
The other issue is the earth cable. Now we don't have the earth conductor or earth block. The earth cable goes direct to the fuse board from cut out. The current earth cable doesn't comply even with 16mm tails. I believe it should be 10mm in the current settings and if upgrading to 25mm cable it should be 16mm. Even this wasn't pointed out to us by the meter installer. May be it's not their job to change the cables but at least during the installation, they should be inspecting that equipment is in compliance. Or is it that my equipment is still in compliance because new regs don't apply retrospectively. Anyway when suppliers installer comes to fit isolator and decides that 16mn tails are good enough, shouldn't then who ever is responsible, change the cut out fuse to the correct rating. Although upgrading the tails should be the best option.
Now some electricians have no problem to upgrade the earth cable and some just getting out of it by saying they don't touch the cutout as this 2nd electrician said. It also makes me wonder that how he was going to change the CU without any isolation because he didn't knew that I had arranged for an isolator to be fitted. I think I should at least ask one more quote and see what he/she can or can't do.
All this brings up new questions. All the CUs come with 100 amp isolators. Do we still need an isolator inside the CU, if one fitted outside, if yes should it be lower rating than the 100amp?
Thanks.