Hi
I don't know if I should ask it here or the main electricians forum. It's about CU change and the work around it and the CU change will be done by a proper registered electrician.

I will try to upload the pictures so you can see what I am talking about. I took two quotations. One just ask for pictures and quoted me for new BG CU with RCBOs, meter tails, upgrade the earth cable as the old one is only 6mm.

The second one visited my house today and after looking at the meter fuse board gave me two quotes, one including materials and one just his labour, testing and certificate charges. He said there is no need to tell Building control as he is registered and his certificate covered it. His quote includes fitting new CU and meter tails. But he said he won't change the earth cable as that is coming out of cut out and he isn't allowed to touch that. He also told me that the tails from the cutout to the meter and then to the fuse board are 16mm. The cutout fuse is rated 100A. The length of tails from cutout to meter is about 60cm and from meter to the fuse board is about 120cm including all the bends. Is all this acceptable? I know that I can ask him to fit 25mm tails to the CU but who is responsible to change the tails from cutout to the meter and who is supposed to change the earth cable for bonding from cut out to the gas pipe.

I have an appointment scheduled with British Gas to fit an isolator between the meter and fuse board as the first electrician asked for it. Can British Gas electrician change the tails and earth bonding cable from cutout while fitting the isolator?
Sorry for a long description and questions.
Thanks
 

Attachments

  • IMG_20210304_155248.jpg
    413.6 KB · Views: 134
  • IMG_20210304_145207.jpg
    297 KB · Views: 111
  • IMG_20210304_145310.jpg
    236.9 KB · Views: 102
  • IMG_20210304_155439.jpg
    250.3 KB · Views: 126
Just to add that the reason he give me quote for labour work is because I asked him to fit Type A and B curve Wylex Rcbos. As he normally installs BG boxes, he said I should purchase whatever I want and he will install it. He is working with my neighbor, doing electrical work on council properties, so I know he is legit. But I don't know if he just avoiding the extra work of changing earth bonding etc or he really isn't allowed to do that.
 
Sorry another correction. The earth cable from cutout is going to the fuse board not the bonding. So my electrician surely can upgrade the earth bonding from the new CU if not from cutout. This raises another question that in the last two years has and water pipes were changed to plastic at the street. From the street it still old water pipe which is lead and the plastic gas pipe was inserted in the existing metal pipe up to the gas meter. Gas meter is only 3 feet away from Electricity meter. Do I still need earth bonding?
Thanks
 
I took two quotations. One just ask for pictures and quoted me for new BG CU with RCBOs, meter tails, upgrade the earth cable as the old one is only 6mm.

The second one visited my house today and after looking at the meter fuse board gave me two quotes, one including materials and one just his labour, testing and certificate charges. He said there is no need to tell Building control as he is registered and his certificate covered it. His quote includes fitting new CU and meter tails.
the sparks that going to do the work does that include a EICR first before the work is Done.
 
Just to add that the reason he give me quote for labour work is because I asked him to fit Type A and B curve Wylex Rcbos. As he normally installs BG boxes, he said I should purchase whatever I want and he will install it. He is working with my neighbor, doing electrical work on council properties, so I know he is legit. But I don't know if he just avoiding the extra work of changing earth bonding etc or he really isn't allowed to do that.
Is the spark working for some one or working for him self, if working for someone their company might not cover them for working on the side. The questions I would be asking.
 
This work is notifiable under Part P, any electrician who is a member of a scheme can notify for you if they're registered to do so.

From the service head to the meter is not your responsibility as this equipment belongs to the DNO and your energy supplier, from the meter is up to you to maintain. As you're getting an isolator switch fitted your electrician can connect from that, the person fitting the isolator should inspect their equipment before any work is carried out by them to ensure it is safe to do so.

You appear to only have bonding connections to the gas/water and no main earth? Can you post an overall picture of your equipment from the suppliers head to your distribution board?
 
Earth connection from the service head shown in Pic one and two, don't know where it goes too though, or where what I assume to be bonding on the Water pipe?
 
tails from cut-out to meter are the responsibility of DNO. (SSE?).
nothing wrong with a BG board with their compact RCBOs.
upgrading main earth is no problem for a sparks.
bonding cables are for your sparks to upgrade if required.
 
There is a braided earthing conductor with a "Do Not Remove" tag over it into the bottom of the earth terminal.
 
In response to buzzlightyear. Thanks for your reply.
I don't know if he is going to do EICR before doing any work but as I remember our conversation, EICR was never mentioned. He did say EIC after the installation and test. Again I don't know which test/tests will be done.

My next door neighbor is a builder working for the council and renovating the council properties from scratch. This electrician is his friend and also does the work for him. I don't know if he is independent or working for a firm. I'll surely ask more questions. I have seen his work next door and that seems fine to the naked eye.
Thanks
 
Thanks Strima, telectrix and westward10.
I thought the earth cable from cutout with the tag "Do not remove" is the main earth and it is going in to the fuse board, routed behind the ply board. My understanding is that my electrician should upgrade the tails to 25mm from the meter to CU, regardless what is from the cut out. He should also be able to upgrade the earth bonding from the CU to gas/water pipe provided I still need it as the street pipes are plastic.

What can I ask the suppliers electrician other than his usual work of fitting an isolator. Obviously he is going to take the fuse out for a safe work environment. If I supply him the tails and earth cable, can he change them. Obviously a lot will depend on his mood and schedule.
Here is the pic as requested.
 

Attachments

  • IMG_20210304_165639.jpg
    450.9 KB · Views: 115
Just realised that If an isolator is fitted then my electrician can't change the tails from the meter, he can only change from the isolator. So now definitely I will have to ask the supplier's electrician,vif he can upgrade the cables. I will get the cables anyway, whether he does or not.
 
Thanks Mike Johnson. That earth cable from cutout is going in to the fuse board and then another one of same size comes out up to the gas pipe. From this joint of gas pipe it just goes underground to the kitchen, possibly to the water pipe.
 
The installer who fits the isolator should fit the correct size tails, but they may only do this from the meter.

This diagram shows you who is responsible for each bit, it's taken from a DNO guide:

Capture.JPG
 
Thanks Strima.
The suppliers installer will fit the correct cables if he deemed necessary. between meter and isolator and between cutout and meter as anything after cutout to meter is the suppliers responsibility.

Now I could be completely wrong but isn't that with a 100 amp fuse the 16mm tails aren't suitable as they have maximum rating of 80amp. We had smart meter fitted April 2020. I am just wandering that why they didn't upgrade the right tails or downgrade the cut out fuse that time. That time I knew nothing about any standards or regulation otherwise I would have asked the installer for this and would have arranged for an isolator at the same time.
The other issue is the earth cable. Now we don't have the earth conductor or earth block. The earth cable goes direct to the fuse board from cut out. The current earth cable doesn't comply even with 16mm tails. I believe it should be 10mm in the current settings and if upgrading to 25mm cable it should be 16mm. Even this wasn't pointed out to us by the meter installer. May be it's not their job to change the cables but at least during the installation, they should be inspecting that equipment is in compliance. Or is it that my equipment is still in compliance because new regs don't apply retrospectively. Anyway when suppliers installer comes to fit isolator and decides that 16mn tails are good enough, shouldn't then who ever is responsible, change the cut out fuse to the correct rating. Although upgrading the tails should be the best option.

Now some electricians have no problem to upgrade the earth cable and some just getting out of it by saying they don't touch the cutout as this 2nd electrician said. It also makes me wonder that how he was going to change the CU without any isolation because he didn't knew that I had arranged for an isolator to be fitted. I think I should at least ask one more quote and see what he/she can or can't do.

All this brings up new questions. All the CUs come with 100 amp isolators. Do we still need an isolator inside the CU, if one fitted outside, if yes should it be lower rating than the 100amp?

Thanks.
 
100A is the max. rating of the cutout fuse holder. 100A fuses were common several years ago, but the DNOs have been changing them to 80A when the opportunity arises on 'normal' supplies.
 
Earlier telextrix said that BG CUs are good. Sorry I didn't meant that BG boards are bad. It's that he was going to get the BG CU from Screwfix and all the prepopulated BG CUs with RCBOs they sell come with Type AC RCBOs. I want Type A RCBOs and I was thinking to get the wylex ones from TLC. Anyway now I found that TLC does sell BG brand Type A RCBOs as well and it comes around £107 pound cheaper than Wylex, it's not that big difference.. Now it's just a struggle to chose between Wylex and BG.
Thanks
 
Thanks brianmooore. So do you think that when smart meter was fitted, they would have changed the fuse. Do they not put any notes etc about the rating of the fuse as I don't see anything to indicate. Do you think that someone should have pointed out that earth cable needs changing.
Thanks
 
It is not necessarily the case the earth cable needs changing. The braided earth is supplied from the DNO and it is their equipment. The energy supplier (in theory) should not touch the DNO equipment and vice versa. It depends on the fault current likely to occur at the CU. Personally I would not fit BG my experience with them has been they are unreliable and I have had quite a few failures with their RCBO. The earth cable from the DNO supplied earth to the CU can be changed no problem but then there must be a reason to do so such as thermal damage for instance. Why are you changing the CU anyway?
 

Reply to New CU and meter tails etc in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Looks very strange to me. Obviously had a new fuse carrier fitted to it at one point but the two cables on the left go to the meter as normal...
Replies
3
Views
711
On a new build site how/ why are people getting away with installing meter tails over 3metres in length and behind dot and dabbed walls with no...
Replies
7
Views
2K
Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
828
Morning all, Really hoping to get some advice / confirm what a few of us are thinking about a job in the future. Back ground - We have to swap...
Replies
15
Views
407
Was helping a friend out and changing their CU which had a date stamp from 1990. Good quality Merlin-Gerin unit and a nice job originally. They...
Replies
7
Views
818

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock