Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes in future. Tails are below the 3m. DNO have agreed to pull fuse to facilitate this work. Timing is perfect as they want to update meter and head. Such as switch will come in it's own enclosure. I assume under 18th Edition regs this needs to be non combustible material ie metal construction. I see alot of double pole switches even one by Wylex all of which are ABS plastic. If metal this will obviously also need to have an earth. Any recommendations of devices to use?
 
Hi, 421.1.201 refers to 'consumer units and similar switchgear' in domestic premises.
The service isolator has generally not been considered to fall within this description., and the DNOs fit plenty that are not metal.

To my thinking it is preferable for it to be a non-conductive material, with a couple of earthing systems having their own 'good reason':
PME - you want to be able to turn it off without a metal enclosure being live if open PEN conditions exist
TT - a fault from Line to the container inside the service isolator wouldn't clear.

So I'd just use the products on the market, with the Wylex REC2 being quite popular.
 
Hi, 421.1.201 refers to 'consumer units and similar switchgear' in domestic premises.
The service isolator has generally not been considered to fall within this description., and the DNOs fit plenty that are not metal.

To my thinking it is preferable for it to be a non-conductive material, with a couple of earthing systems having their own 'good reason':
PME - you want to be able to turn it off without a metal enclosure being live if open PEN conditions exist
TT - a fault from Line to the container inside the service isolator wouldn't clear.

So I'd just use the products on the market, with the Wylex REC2 being quite popular.
Yes I was honestly thinking about going down that line. I have TNCS and aware having an earthed isolator could have issues if broken PEN was to occur. Thankyou.
 
Hi, 421.1.201 refers to 'consumer units and similar switchgear' in domestic premises.
The service isolator has generally not been considered to fall within this description., and the DNOs fit plenty that are not metal.

To my thinking it is preferable for it to be a non-conductive material, with a couple of earthing systems having their own 'good reason':
PME - you want to be able to turn it off without a metal enclosure being live if open PEN conditions exist
TT - a fault from Line to the container inside the service isolator wouldn't clear.

So I'd just use the products on the market, with the Wylex REC2 being quite popular.
If considering the open PEN wouldn't that therefore apply to all consumer units with a main isolator
 
The one I have kicking around still to be used in the Wylex RECSW2S which is slightly slimmer, and more importantly it has double clamp screws for each cable.

I think the main issue that prompted the regs to push for non-combustible enclosures was badly terminated connections overheating, so a combination of dual screws and the correct torque setting, plus a bit of settling/wiggling/re-checking torque should largely eliminate that risk.
 

Attachments

  • 1708116328265..jpg
    182.2 KB · Views: 5

Reply to Mains Isolator advice in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Hi all, if I cannot access the line side of a crabtree 100A DP main switch. Would someone enlighten me how to conduct safe isolation on this...
Replies
15
Views
1K
Hi there, Any advice on this would be greatly appreciated! (Note, this is not a DIY, I'm using a fully qualified electrician, just posting here...
Replies
8
Views
643
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
0
Views
1K
Deleted member 155212
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock