Hi all, if I cannot access the line side of a crabtree 100A DP main switch. Would someone enlighten me how to conduct safe isolation on this installation. Would the main fuse need to be removed ? Thankyou.
 

Attachments

  • IMG_0114.jpeg
    IMG_0114.jpeg
    9.5 KB · Views: 90
https://www.----------------------------/media/blak1wkt/best-practice-guide-2-issue-4.pdf
 
What is it you are wanting to do?
 
  • Like
Reactions: Rob678 and DPG
What is it you are wanting to do?
Conduct safe isolation of the consumer unit. However once I have proved my my voltage meter works. How would I be able to conduct L-N, and L-E on the consumer side of the main switch ? The face of the screw is covered by plastic
 
Safe isolation to replace it, work on it?
 
  • Like
Reactions: Rob678
Safe isolation to replace it, work on it?
Neither in this instance. Just purely interest. So far in my apprenticeship we have always been able to conduct the safe Isolation tests on L-E L-N and N-E. As I can use my voltage detectors on the non-supply side of the main switch. I don’t understand how I would be able to conduct safe isolation on this main switch to ensure the board is safe to work on if I was to remove an mcb or RCBO ? I understand if I needed to remove the main switch DNO would need to be contacted as that involves work on the supply side.
 

Attachments

  • IMG_0114.jpeg
    IMG_0114.jpeg
    9.5 KB · Views: 64
  • IMG_0118.png
    IMG_0118.png
    628.2 KB · Views: 69
Ah, so your enquiry relates soley to the pictured Isolator, with missing terminal to test at.
What make is it?

1697563447463.jpeg
 
That is an isolator for a Crabtree Starbreaker CU. The only way you can prove the outgoing side is dead is at the protective device terminal as the live terminal from the isolator plugs onto a busbar.
 
Presumably a crabtree starbreaker CU where everything plugs into the shrouded busbar?

I think you would have to use the outgoing terminals of the protective device(s)
 
Presumably a crabtree starbreaker CU where everything plugs into the shrouded busbar?

I think you would have to use the outgoing terminals of the protective device(s)
Yes Dave that is correct. That’s the only solution in my head I could come up with. But I thought surely there must be another route ? Have looked for many sources online but couldn’t find an answer.
 
Why would you need another way?

This is a genuine question as there is an argument you could make as to a, very unlikely, scenario which could make this method unsuitable.
I suppose you wouldn’t. I meant that question more in the sense I felt like I’d be doing something wrong as I have always completed SI from the Main switch in this scenario
 
I suppose you wouldn’t. I meant that question more in the sense I felt like I’d be doing something wrong as I have always completed SI from the Main switch in this scenario

OK, so the very unlikely scenario is the MCB going faulty at the same time as you open the main switch, this could give a false result on your safe isolation test.

This is an incredibly unlikely thing to happen and you can mitigate it by testing at multiple protective devices just to be sure.
 
OK, so the very unlikely scenario is the MCB going faulty at the same time as you open the main switch, this could give a false result on your safe isolation test.

This is an incredibly unlikely thing to happen and you can mitigate it by testing at multiple protective devices just to be sure.
Thankyou Dave 👍🏽
 
  • Like
Reactions: DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Hampshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
How to conduct safe isolation on this main switch ?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
Rob678,
Last reply from
Rob678,
Replies
15
Views
2,107

Advert