Again, I'm hoping this is in the right forum. If not, please don't hesitate to say so...

That said, the back story is that I just bought a new dryer. Because I'm an idiot, I didn't check the power cord before purchasing, and now that it's in my home I notice that it has a nema 14-30 plug. I don't have a 14-30 outlet in the apartment, although I do have 2 normal north american 3-prong outlets next to the dryer and what looks like a 14-50 outlet across the room that the stove is plugged into.

Is there a solution to this? Is it possible to adapt the normal 3-prong outlets or even the nema 14-50 outlet? Is there another option? Or should I pull my hair out and sell the dryer?

Thanks so much for any help. I'm really a newbie. Thanks again.
 
Erm, are you in the US?
If so you may not have much joy as this is a UK site!!! That aside though someone may be along in a bit who does know!
 
Ring the store you bought it from and see if they sell an adapter for it or ring a local electrician as per the above post we are UK based.


Good luck


Chris
 
Dont cut the plug of or change it if you have similar laws to us you will invalidate your warranty.


Chris
 
Again, I'm hoping this is in the right forum. If not, please don't hesitate to say so...

That said, the back story is that I just bought a new dryer. Because I'm an idiot, I didn't check the power cord before purchasing, and now that it's in my home I notice that it has a nema 14-30 plug. I don't have a 14-30 outlet in the apartment, although I do have 2 normal north american 3-prong outlets next to the dryer and what looks like a 14-50 outlet across the room that the stove is plugged into.

Is there a solution to this? Is it possible to adapt the normal 3-prong outlets or even the nema 14-50 outlet? Is there another option? Or should I pull my hair out and sell the dryer?

Thanks so much for any help. I'm really a newbie. Thanks again.

Having worked in the US I am going to try and give you an answer.

You can not use your nema 5 (normal 3 prong outlets) as these are 115V outlets and your appliance is 230V.
I would not recommend that you try to adapt your lead to a nema 14-50 socket as this is rated and protected at 50A and is generally used for cookers.
What you could do is replace your 14-50 outlet with a 14-30 and install a 30A circuit breaker.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
New dryer
Prefix
N/A
Forum
Electrical Appliances & Whitegoods Forum
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
Papa,
Last reply from
Sintra,
Replies
6
Views
1,383

Advert

Back
Top