I'm a new member to the forum so thought I'd introduce myself.
Been qualified for around 10 years and have finally set up on my own. I am new to the test and inspection side of things so I am seeking advise on the following question. Any help would be greatly appreciated.

A friend of my misses is buying her first property and the seller has had a EICR completed. Now the question is that the installation is recorded as a TN-S with a Ze of 2.1 ohms.

My understanding is that the Ze for a TN-S is 0.8 ohms. Am I missing something or is this reading excessively high?

Any help/advice appreciated

Regards

Clarkie
 
The EICR chaps will be along shortly, in the meantime you are correct that the Ze for a TN-S system is around the 0.8 figure, although in may be higher in rural areas.

Perhaps the home owner should ask the DNO for advice on this matter. They may say it is what it is, and are not obliged to improve it. What did the EICR suggest?
 
This is an interesting question no doubt..... The EICR forms allow you to comment on the incoming service supply but they are technically outside the scope of the EICR.

I would have commented.

Such a high Ze would mean all 20a and above circuits would exceed their max Zs so there must be RCD's installed.

Calling the DNO may result in them not doing anything.....
 
Will upload the EICR later on, but in answer to Midwest yes they did a Zs on both final rings with the same reading of 0.39 ohms

The property must have some chunky metal service pipes in, or the Ze is incorrect. What do ya think EICR warriors?

Have you considered contacting the DNO and asking them, they won't bite and usually will come and have a butchers for free.
 