dave30

hello im replacing a 7.5 kw shower that has a 6mm csa line and neutral cable with a 2.5 mm csa cpc on a 40amp mcb instalation method 102 in a stud wall with instalation cabble touching wall




with a 9.5 kw shower with a 10mm csa line and neutral cable with a 4.0 mm csa cpc on a 45amp mcb instalation method 102 in a stud wall with instalation cabble touching wall



so 9500 / 230 = 41.3 means i need a 45 amp mcb 10mm csa twin and earth


can someone please confirm if this correct its a job im doing next week


thanks again
 
sounds right, but you would most likely get away with a 40A MCB. many manufacturers don't do 45A.
 
if you can get a 45A to match the CU then go for the 45A. i weas just pointing out that with a lot of manufacturers you can't get 45A and a 50A might be too high for 10mm installed to ref.103. ( not got regs to hand )
 
9500 / 240 = 39.9A probably stated by manufacturer

equates to

8740 / 230 = 38A values used for circuit design.

Although it makes no difference in this case.
 
Ref method 102 10mm = 47amps

you might also be interested in volt drop/fault protection/ thermal constraints
Try this

Ib<In<Iz
Ib = design current
In = rated current of protective device
Iz = current carrying capacity of cable in its installed condition

then
Max cable length for volt drop = 11.5 x 1000 / Ib x(mV/A/m) x Ct

(mV/A/m) for 10/4mm in OSG
Ct will be 1

then
Fault protection max length = Zs maximum BS7671 - Ze /(R1+R2) x Cr
(R1 +R2) for 10/4 mm in OSG
Cr = operating temp Table in OSG (usually 1.2)

then Adiabatic for thermal constraints of cpc
S > or equal to square root of I squared t /K

S = csa of cpc in mm
I = fault current (230v/Zs)
t = duration in seconds of fault current (0.1sec in your case)
K = factor from BS7671 (T&E = 115)

Hope this helps
 