Ditch the consumer unit in the summer house it is not required. Spur from the ring final through a fuse connection unit then swa to summer house socket then onto the garden socket. It will be limited to 13A but this is probably fine, you just need to correctly size your cable for volt drop.
In the OP's case this will also be preferable to running a new circuit from the house CU, as the latter would be notifiable.
Hi Barrett’s,
Just looks at your quals.
I think it may be a good idea to get in contact with an experienced spark who could mentor you on site for a small fee maybe. Maybe get him or her to design install and you do install. This way you would benefit from the experience.
Somewhat of a failing to understand the fundamentals of design & installation. And you are proposing to charge someone for this service.
@Barreoty take the good advice, and go and work for an experienced electrician or company,to gain some valuable experience. You are not at the point where you go carry out these installs on your own. Sorry to be harsh.
The design is not great but not unsafe.
Get rid of the CU and the 1.5mm cable. Run the 2.5 swa directly from the fcu to the two socket outlets.
If the customer does not want new circuit running through the house then there's nothing else to be done.