Hi. My first post.
I can't find information specific to Vaulted ceiling safe zones in the regs.

I've posted a diagram below but not sure what size it will display as.

My question is: For a vaulted ceiling are the sloping sections of wall within 150 mm of the top of the wall and ceiling junction a safe zone?

Many thanks


Vaulted ceiling safe zone 2.JPG
 
Yes from me as well. The wording of the regulation is "150mm from the top of the wall"

Personally It's not an area I like to run cables whatever angle of ceiling though. I only install there as a last resort mainly because it's usually more work and repair involved as well as the general lack of awareness of safe zones amongst anyone but those who install cables.
 
The whole of the space above a ceiling or below a floor is considered a safe zone.
Except where a cable runs through a joist or batten.
Where cables run through joists or battens, the requirement is for the depth to be greater than 50mm, or for there to be an earthed sheath or mechanical protection.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Newcastle upon Tyne

Thread Information

Title
Newbie. Vaulted ceiling safe zone
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6
Unsolved
--

Advert

Thread statistics

Created
loopin7,
Last reply from
DPG,
Replies
6
Views
5,614

Advert

Back
Top