Customer says the lights in two upstairs rooms have stopped working. I’ve checked the wall switches in both rooms and there is power to both but both wires in switch are showing current, operating the switches makes no difference? The rooms both have downlights so no ceiling roses to check, my first thought was a previous light in the circuit has been wired wrong but the RCBO has not tripped on this circuit
 

Strima

-
Arms
Esteemed
JB somewhere with a dodgy joint in it.
 
  • Thread Starter Thread Starter
  • #6
Or a dodgy connection at a switch or lighting point!!
Customer says no work done elsewhere, the lights are wired up whereby the switches operate the lights via a switch wire connected to the lights and not wired whereby the power goes through the switch. Why would I detect current on both sides of the switch wire when I’ve disconnected the switch
 
  • Thread Starter Thread Starter
  • #8
Customer says no work done elsewhere, the lights are wired up whereby the switches operate the lights via a switch wire connected to the lights and not wired whereby the power goes through the switch. Why would I detect current on both sides of the switch wire when I’ve disconnected the switch
Do you mean "current" or actually voltage? If voltage, a broken neutral somewhere perhaps?
I only had a short amount of time on Friday to check , back there tomorrow to investigate further. If there was a problem with the neutral wouldn’t this trip the RCBO?
Post automatically merged:

What's led up to the lights not working? Any work done elsewhere?
Customer said no work done elsewhere, they just stopped working
Post automatically merged:

Someone put a new light up, miswired at a prior light?
That’s what I thought at first but customer said nothing done. Both wires of switch wire showing as live at switch end, with switch disconnected
 
Last edited:
Forget rcbo issues you almost certainly have a lost connection on the loop circuit.
 

James

-
Mentor
Arms
Supporter
Esteemed
That’s going to be my next step,dead testing. Just puzzled as to why I detect both wires at switch as live when not connected to switch
What are you using to test it and prove it is live?
 

davesparks

-
Mentor
Arms
Esteemed
That’s going to be my next step,dead testing. Just puzzled as to why I detect both wires at switch as live when not connected to switch
There is likely to be a broken neutral somewhere in the circuit.
So obviously with any load connected in the circuit the neutral conductor downstream of the break will be at line voltage as it is connected to the line conductor via the load.

This is assuming you have confirmed this is not a phantom voltage you have measured?
 
  • Thread Starter Thread Starter
  • #19
Please don't say that is a neon indicating screwdriver.
It was 😬, it was end of the day my testers had been put back in the van, so this was just a quick look. Tomorrow look at it more in depth, just wondering if anyone has had the same issue
 

telectrix

-
Mentor
Arms
Esteemed
should have left the tester screwdriver in the van, along with the tea and sugar pots. coz. all it's fit for is stirring tea.
 