as i expected most of my domestic work would be rewires,cu changes and fault finding i am a bit concerned that i have had three intermitent rcd faults in the last week? 1 solved other ongoing appliance i think? another going to look at tommorow.
as for the appliance i was thinking i should be able to pat test but i don't know how so have been looking into pat testing.
next i have been looking into earth leakage clamp meters but as money is tight don't know which to prioritise any ideas?
 
Try doing a ramp test on RCD at source with no loads connected compared to a ramp test with loads connected. The difference between the 2 readings will be the approximate earth leakage of the equipment.
 
as sintra says....ramp suspect RCDs...this will give the actual level of leakage required to trip the RCD....
its the first thing that you should do....verify the RCD is ok first before anything else...this includes blaming it on connected loads/appliances....unless of course that its patently obvious that an appliance etc is the cause...
anything below 15mA should be discarded as its likely that the device will deteriate in the future and you`l only end up going back in a few weeks time...
the manual test button should also be operated to ensure its working
 
ok first nuisance failed rcd ramp test so new rcd no probs,second rcd failed and failed manual reset so replaced but still fault so put two circuits on non rcd side and new kitchen tripping rcd so if i ramp test while on load each appliance i will find fault, thanks.
next i have a boiler tripping rcd but will have to look at it if it is the boiler and not the wirring to any ideas of typical reasons?
 
ok first nuisance failed rcd ramp test so new rcd no probs,second rcd failed and failed manual reset so replaced but still fault so put two circuits on non rcd side and new kitchen tripping rcd so if i ramp test while on load each appliance i will find fault, thanks.
next i have a boiler tripping rcd but will have to look at it if it is the boiler and not the wirring to any ideas of typical reasons?
yes...first verify the feed to the boiler is in good order....
went to a place a while back....55 volts sitting on some pipework...it was a redundant 2.5 feed to the old immersion heater that had been left energised....
the point i`m making here is that feeds to immersion heaters are often run parrallel to hot pipes....and after the immersion heater & cylinder have been removed the old feed is used for the new boiler...so its always prudent to check first before anything else of you have verified its that circuit thats givin jip
 
now...if its the boiler itself thats causing the problem....you will have to ask someone in here with more experience than me about boilers...as theres several issues with them i think that are known causes of tripping RCDs...apart from the obvious that is...
 
ok first nuisance failed rcd ramp test so new rcd no probs,second rcd failed and failed manual reset so replaced but still fault so put two circuits on non rcd side and new kitchen tripping rcd so if i ramp test while on load each appliance i will find fault, thanks.
next i have a boiler tripping rcd but will have to look at it if it is the boiler and not the wirring to any ideas of typical reasons?
IR test this...
not the RCD..lol...
 