Hi all.
I'm having an Issue with a family members board.
They have had either the breaker for a ring or the RCD trip on numerous occasions, and I have already replaced a socket where the neutrals connections were burned out on said ring.
So I went to run a few tests to see if I could find the problem. I don't have much experience in the way of testing or fault finding as there has always been someone else on site that does that, but I need to pull my finger out and crack on with getting to grips with it.
I started by finding out what was running off that ring....20 double sockets...two under floor heating systems and the heating/hot water for the house. three of those double sockets were single point spurs, and then spurred off the heating...two lighting points.
I ran an end to end at the DB and got a reading for live and earth but nothing on neutral ( so open neutral.....somewhere??) I have removed every socket and switched fuse spur that is on that circuit and all looks good, no screws through the insulation...nothing. so I know something about connecting only one side of the ring back into the breaker (making safe the other ends) and then testing at each socket around the house....but this is where I am a bit lost. I need a clarification as to what I am looking for and maybe a bit of why. I left the installation with the ring ends removed from the board and a temp supply from a working ring to feed the heating and hot water, but I want to nail this one asap
thanks in advance people ....Dray
I'm having an Issue with a family members board.
They have had either the breaker for a ring or the RCD trip on numerous occasions, and I have already replaced a socket where the neutrals connections were burned out on said ring.
So I went to run a few tests to see if I could find the problem. I don't have much experience in the way of testing or fault finding as there has always been someone else on site that does that, but I need to pull my finger out and crack on with getting to grips with it.
I started by finding out what was running off that ring....20 double sockets...two under floor heating systems and the heating/hot water for the house. three of those double sockets were single point spurs, and then spurred off the heating...two lighting points.
I ran an end to end at the DB and got a reading for live and earth but nothing on neutral ( so open neutral.....somewhere??) I have removed every socket and switched fuse spur that is on that circuit and all looks good, no screws through the insulation...nothing. so I know something about connecting only one side of the ring back into the breaker (making safe the other ends) and then testing at each socket around the house....but this is where I am a bit lost. I need a clarification as to what I am looking for and maybe a bit of why. I left the installation with the ring ends removed from the board and a temp supply from a working ring to feed the heating and hot water, but I want to nail this one asap