Hello

I have an outbuilding which has its own earth rod, but I am getting a 280ohm ze.

I have checked the ze in the main building and it is 150.

The earth in the 3 core SWA supplying the outbuilding is not being used, is there any reason or part of the regs that says I can't use the main building earth (rod)

I want to avoid banging in another parrallel rod at all costs as there is a lot of cotswold stone its impossible to get anything in.

thanks

Tom
 
There is nothing wrong with using the main building earth rod derived MET via your 3-core SWA.
 
Ok thank you, I am now getting a reading of 155ohms which is good.

Now, Would i be expected to check continuity of the earth from the main house to the outhouse? (in a run through the tests when you would normally check continuity of main earth)

Is the efli test (ze) enough (for the niceic assessor) as I have never used the stakes in ground method and do not have the kit..

thanks for the help much appreciated
 
Ok thank you, I am now getting a reading of 155ohms which is good.

Now, Would i be expected to check continuity of the earth from the main house to the outhouse? (in a run through the tests when you would normally check continuity of main earth)

Is the efli test (ze) enough (for the niceic assessor) as I have never used the stakes in ground method and do not have the kit..

thanks for the help much appreciated

Tom, I would urge you to obtain a copy of Guidance Note 3, all of your points are covered and you can be confident in your testing at your assessment.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Outbuilding earth rod
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
5
Unsolved
--

Advert

Thread statistics

Created
tomchester999,
Last reply from
tomchester999,
Replies
5
Views
2,016

Advert